    30 ton split R-22 to 410a

    30 ton split system using existing 30 year old coils. All lines left in as well as accumulator. Txv's were replaced as well as liquid line solenoids. Suction line filter added and lines blown with nitrogen. How much left over oil in the system is acceptable? The coils had to stay I wish it could have been replaced. Holes were drilled in the traps and taps were added so oil could be drained and blown out with nitro. Thoughts and feelings? Unit is not fired off yet. I am thinking of removing accumulator, and flushing with a flush kit.
    I STARTED WITH NOTHING, AND I STILL HAVE MOST OF IT!

  2. #2
    Join Date
    Mar 2011
    Posts
    1,075
    Post Likes
    Pretty sure this is a huge mistake.

  3. #3
    Join Date
    Apr 2007
    Location
    uk
    Posts
    254
    Post Likes
    You need to take a step back and think about this.
    UNDER NO CIRCUMSTANCES START THIS UNIT UP WITH R410A.
    None of the components will be rated for R410A and are likely to fail using R410A.
    If you want to change out R22 then you need to change to a compatible refrigerant USING SIMILAR PRESSURES such as R417A R422D depending on size of unit.

    This is an accident waiting to happen.

  4. #4
    Join Date
    Nov 2005
    Posts
    1,351
    Post Likes
    Thread Starter
    Quote Originally Posted by Gibbo View Post
    You need to take a step back and think about this.
    UNDER NO CIRCUMSTANCES START THIS UNIT UP WITH R410A.
    None of the components will be rated for R410A and are likely to fail using R410A.
    If you want to change out R22 then you need to change to a compatible refrigerant USING SIMILAR PRESSURES such as R417A R422D depending on size of unit.

    This is an accident waiting to happen.
    condensing unit is installed and is 410. I think we have to use 410 t this point.
    I STARTED WITH NOTHING, AND I STILL HAVE MOST OF IT!

  5. #5
    Join Date
    Apr 2010
    Location
    southern california
    Posts
    535
    Post Likes
    Quote Originally Posted by AiResearch View Post
    Pretty sure this is a huge mistake.
    I tend to agree.The coil parameters are not even close between R-22 and 410. As far as accumulators goes, it needs to be resized for the change in refrigerant. Accumulators are inexpensive compared to compressors.These are the types of jobs that any good service company would love to chase. Lots of problems, and there is nothing like doing the job twice.

  6. #6
    Join Date
    Sep 2005
    Location
    Atlanta GA area
    Posts
    36,247
    Post Likes
    Quote Originally Posted by acwizard View Post
    I tend to agree.The coil parameters are not even close between R-22 and 410. As far as accumulators goes, it needs to be resized for the change in refrigerant. Accumulators are inexpensive compared to compressors.These are the types of jobs that any good service company would love to chase. Lots of problems, and there is nothing like doing the job twice.
    Seems I end up doing it the second time... after the first contractor has a phone number change...

    I appreciate hacks (not referencing anyone)... they make me lots of $$$
    GA-HVAC-Tech

    Your comfort, Your way, Everyday!

  7. #7
    Join Date
    Mar 2007
    Location
    South Texas
    Posts
    239
    Post Likes
    Recently did a conversion on two 20 ton units as the condensers needed replaced. Warned the customer not to do it turns out we were right chasing refrigerant leaks on the indoor coil that were not there when the conversion was done. Big mess

  8. #8
    Join Date
    Oct 2001
    Posts
    6,966
    Post Likes
    both ends of the system was tested for R-22 now its going to see and feel 410A oil is the least of your problems,rebraze all the lines and do a 1000PSI nitro test maybe tonnage has to be effected with the higher pressures in what could be considered a low pressure original install
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY

  9. #9
    Join Date
    Sep 2005
    Location
    Atlanta GA area
    Posts
    36,247
    Post Likes
    Seems to me a lot of similar refrigerants to R22 are available. I would be seriously worried about the system not handling the higher pressures.

    Your prep sounds good... however a refrigerant that both operates at similar pressures and uses mineral oil would be my choice.

    Let us know how this works out.
    GA-HVAC-Tech

    Your comfort, Your way, Everyday!

  10. #10
    Join Date
    Nov 2005
    Posts
    1,351
    Post Likes
    Thread Starter
    I will say this job got dropped in my lap to wrap up and fire off. I have checked the majority of all the brazed joints and have a 450 psi test on it right now. I am just trying to make the best of a bad situation. I had heard there were some new schools of thought about actually leaving oil in the system. I am curious if anyone had done it. The job has to be fired of on Tuesday regardless of what I want, it is out of my hands.
    I STARTED WITH NOTHING, AND I STILL HAVE MOST OF IT!

  11. #11
    Join Date
    Jun 2006
    Location
    New Jersey
    Posts
    4,393
    Post Likes
    Quote Originally Posted by allstar08 View Post
    I will say this job got dropped in my lap to wrap up and fire off. I have checked the majority of all the brazed joints and have a 450 psi test on it right now. I am just trying to make the best of a bad situation. I had heard there were some new schools of thought about actually leaving oil in the system. I am curious if anyone had done it. The job has to be fired of on Tuesday regardless of what I want, it is out of my hands.
    I haven't done a 22 to a 410a conversion using a unknown rated coil. But with that said, I have done conversions from a mineral to a POE refrigerant. From what you have said, I would skip the flush kit, but change the accumulator for good measure.

    Why is there is an accumulator? And you only have one......is this a single lineset?

  12. #12
    Join Date
    Nov 2005
    Posts
    1,351
    Post Likes
    Thread Starter
    Quote Originally Posted by SouthTex View Post
    Recently did a conversion on two 20 ton units as the condensers needed replaced. Warned the customer not to do it turns out we were right chasing refrigerant leaks on the indoor coil that were not there when the conversion was done. Big mess
    have you had any acid problems? did you reuse the line sets as well as the coils? did you flush the indoor coils?
    I STARTED WITH NOTHING, AND I STILL HAVE MOST OF IT!

  13. #13
    Join Date
    Dec 2005
    Posts
    2,006
    Post Likes
    Quote Originally Posted by allstar08 View Post
    30 ton split system using existing 30 year old coils. All lines left in as well as accumulator. Txv's were replaced as well as liquid line solenoids. Suction line filter added and lines blown with nitrogen. How much left over oil in the system is acceptable? The coils had to stay I wish it could have been replaced. Holes were drilled in the traps and taps were added so oil could be drained and blown out with nitro. Thoughts and feelings? Unit is not fired off yet. I am thinking of removing accumulator, and flushing with a flush kit.
    If you ask this question on the refrigeration forum, they will laugh at it. Because they have done it for years.

    Look like you have done your home work on oil flushing. Let her ripe. How many SEER can you loose? This 30 tons comes off the factory with 9 SEER .

    I agree with you about the accumulator.

Page 1 of 4 1234 LastLast