    replace TXV, new drier and R22 necessary?

    Trane dealer serviced my HVAC. He says the TXV valve is defective, brand is Sporlan. He said this is a well known issue from a certain period.

    Anyway, he wants to replace the TXV but also the drier and put new R22 into the system. Are the drier and R22 necessary or is he trying to get more money out of this repair?

    Is the Sporlan TXV defect really well-known. The system was installed in 2007.
    The problem was AC could not cool the house enough in the afternoons, when it is 100 degrees outside. Morning and night seems OK.

  2. #2
    Join Date
    May 2004
    Location
    Frederick, MD
    Posts
    917

    Did he

    give a reason as to why he wanted to replace the refrigerant? Under normal circumstances, it's not necessary. Replacing the drier is a good thing.

  3. #3
    Join Date
    Mar 2007
    Location
    South Texas
    Posts
    214
    can't trouble shoot the system to know if that's the problem. If we were changing a txv and the drier was in the out door unit, we would recover the refrigerant, change the drier, evacuate and put in new refrigerant

  4. #4
    Join Date
    Sep 2010
    Location
    corona, ca
    Posts
    14
    Might be worrier your old refrigerant is contaminated? He would have to remove it anyways to replace the HS drier filter might as well put new refrigerant in.

  5. #5
    Join Date
    Feb 2011
    Location
    Cloverdale,Ca
    Posts
    305
    Go with what he says if you want his warranty. Otherwise tell him to reuse your R-22 and release him from the liability of warranting his repair.

  6. #6
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,699
    What he is listing is a text book procedure. Most home owners would be thrilled to have someone do their repair by the book. And avoid additional cost later because of corners having been cut.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  7. #7
    Join Date
    Jul 2011
    Posts
    2
    I don't why he wants to change the R22. Looks like he is going to pull all of it then put new R22, about 10-12 pounds. I am not an expert, my first HVAC problem ever. I thought some of the R22 could be recycled into the system. Is it a contamination problem? I called a few other service people, some say replacing the TXV alone might work. Any experience on this? I am trying to see if the drier and full R22 are necessary.

    this unit is in the attic.

  8. #8
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,699
    The factory drier in the condenser requires the charge to be recovered. So he is going to charge with new refrigerant to make sure no contaminates(if there are any) from the old gas are put back in to your system.

    He is performing the work as he should. If he cuts corners. Do you want to pay 3 times as much to fix it again, and again.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  9. #9
    Join Date
    Jul 2010
    Location
    nebraska
    Posts
    1,628
    Quote Originally Posted by ommatidia View Post
    I don't why he wants to change the R22. Looks like he is going to pull all of it then put new R22, about 10-12 pounds. I am not an expert, my first HVAC problem ever. I thought some of the R22 could be recycled into the system. Is it a contamination problem? I called a few other service people, some say replacing the TXV alone might work. Any experience on this? I am trying to see if the drier and full R22 are necessary.

    this unit is in the attic.
    It could be reused if recovered into a clean tank. A new tank costs more then the refrigerant does though. The drier should be replaced.
    Last edited by martyinlincoln; 07-08-2011 at 06:11 PM. Reason: added drier

  10. #10
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    33,884
    We changed out a slug of Sporlans on Trane R22 evaps a while back. Just pumped down the charge, changed the TXV in minutes, pulled a good vacuum with micron gauge and let loose the 22. Didn't see the need to recover, change out the drier in the outdoor unit and use new refrigerant. Had there been a leak that pulled moisture in, yes.

  11. #11
    Join Date
    Jul 2010
    Location
    nebraska
    Posts
    1,628
    Goodness! I was thinking outdoor txv on a heat pump when responding,not thinking is closer to correct. Sorry about that.

  12. #12
    Join Date
    Jun 2011
    Location
    Joliet, IL
    Posts
    21
    If he is a reasonably priced tech, you are getting a great deal.

    If he is an expensive tech, you are getting a great deal.

    Because he is doing it the right way, and there are a lot of techs that would half ass even a simple job like that.

    High-five him for me, please.

  13. #13
    Join Date
    Feb 2008
    Location
    Waffleville
    Posts
    10,339
    if it is a split system, the refirgerant can be pumped down into the outdoor unit and reused, after new valve is installed.

    if it is a heat pump and the outdoor txv is bad, the refrigerant can be reverse pumped down into the indoor unit and the txv and filter drier can be changed and the refrigerant can be reused.

    if you want to continue with the same refrigerant, it can be recovered through a filter drier and then reinstalled into the machine after the service repairs have been made. I do this all the time. However, i will still charge for the additional time and materials, as the filter drier used for this is one time use.
    If Guns Kill People, Do Pencils Misspell Words?

    http://www.youtube.com/watch?v=An2a1...eature=related

    Before we work on artificial intelligence why don't we do something about natural stupidity?

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event