Check your EMAIL , I scanned the flow / pressure drop charts and sent them.
-
07-11-2011, 10:21 AM #15
Yes, any help would be greatly appreciated. Thank you Chet
Here is the info on Chiller #2 that will not chill water down after switching over from #1 chiller that is running fine. Heres the conditions the Chiller #2 is running at right now:
Load set 60%
Evap pressure: 11" Vacuum
Condenser pressure: 10 PSIG
Oil Pressure: 13PSIG
Condenser Refrigerant Temp: 84 DegF
Condenser Water Temp inlet: 73 DegF
Condenser Water Temp outlet: 76 DegF
Evaporator Water Temp inlet: 58 DegF
Evaporator Water Temp outlet: 54 DegF
Condenser Water Inlet Pressure: 52 PSI
Condenser Water Outlet Pressure: 42 PSI
Note: Both chillers had the Condensers tube brushed at the end of last season by another contractor.
Life is too short not to enjoy life to the fullest - Don't be bogged down dealing with difficult people -who try to inflict their problems in life onto you or other good people...
"Instead return the mutual respect to the good people who respect you - Forget about the one's who won't" .....what Chet lives by.....
-
07-11-2011, 12:05 PM #16
Regular Guest
- Join Date
- Jul 2001
- Location
- Canada
- Posts
- 1,694
Did you get the EMAIL ?
-
07-11-2011, 01:20 PM #17Life is too short not to enjoy life to the fullest - Don't be bogged down dealing with difficult people -who try to inflict their problems in life onto you or other good people...
"Instead return the mutual respect to the good people who respect you - Forget about the one's who won't" .....what Chet lives by.....
-
07-11-2011, 04:24 PM #18
Professional Member
- Join Date
- Sep 2008
- Location
- Delaware
- Posts
- 243
So you have 73/76 cond h2o in & out with an 84 degree liquid temp off the cond. These machines were usually at 10/10/10 at full load. That is 85/95/105 on the liquid temps. You are showing 8 degrees delta t on leaving water and liquid ref at 60 % load. Its close but I would expect 5-6 degrees. Your thermo's accurate? Also you are only picking up 3 degrees on the water side. Again I would expect 6 at 60%.
Now looking at the Liquid temp vs cond pressure you have 84 degree liquid which shoud show about 2 psi pressure but you report 10 psi which equates to about 102 degrees.
Sooo, my opinion (remember what you are paying for it) is air in the machine causing high head pressure plus some tube fouling in the cond. The only thing saving your butt is the cold tower water which is depressing the high side and keeping you out of surge ( I presume you are not surging). The cond flow looks good.
Those tubes will only take about .0005" of fouling before pperformance starts going downhill and a machine can foul in about a week under the right conditions.
Check out the purge on this unit. What type of purge is it. Was the chiller down for an extended period of time?
-
07-11-2011, 06:00 PM #19
Professional Member
- Join Date
- Sep 2008
- Location
- Delaware
- Posts
- 243
The evap side looks Ok. You show making 4 degrees thru the bundle with an approach of 2-3 degrees. Check the belly temp and compare it to the evap pressure and leaving chill h2o when you get time. Single pass evaps give some different readings than you might expect.
If you are not doing it, start logging all your readings for your reference!
-
07-11-2011, 07:29 PM #20
the purge unit is a timed style. Yes the chiller has been down for extened amount of time
Life is too short not to enjoy life to the fullest - Don't be bogged down dealing with difficult people -who try to inflict their problems in life onto you or other good people...
"Instead return the mutual respect to the good people who respect you - Forget about the one's who won't" .....what Chet lives by.....
-
05-08-2012, 02:15 AM #21
Professional Member
- Join Date
- Oct 2007
- Location
- Arizona DUH
- Posts
- 164
Email Copy
I saw on this post from last year on flow charts and associated DP settings (ft/hd) for Trane Chillers. I am trying to det up some DP devices for measuring flow and I cannot find the Trane Document online, I saw where you had e-mailed it to someone. Is it possible for you to send this to me as well, I would really appreciate it????
-
05-08-2012, 05:51 AM #22
Moved thread to Tech to Tech commercial.


Reply With Quote