Results 1 to 13 of 14
Thread: Coil with TXV
    Oct 2005
    when using a coil with a TXV and your soldering in the coil what should you do with the sensing bulb????? test question
    burn it up.
    Feb 2005
    Dothan, Al
    nitro
    Remove it from the line or cover it with a wet cloth.
    Richard
    Midlothian, Virginia
    you just did nitro's homework riding
    Goodbyee stranger it's been nice. Hope you find your paradise! Hey it aint rocket science, "It's a Trade !"
    cut it out of the way.
    Oct 2005
    Wrap it in a wet rag or put it down in a glass of ice water. In other words dont damage it in any way
    I don't have any facts to back it up, but my gut fealing is that most of the "warranty" TXV failures that happen are due to installers not protecting the TXV sensing bulb when brazing the vapor line onto a coil or air handler that has a built in TXV.
    Most of the coils and air handlers with built in TXVs have the sensing bulb mounted just a few inches away from where you braze the lines on.
    most TXVs that come
    with the evap coils are crap anyways (can you say Trane?)
    but even then the sensing bulb is clipped on and very easily moved for brazing
    Apr 2005
    illinois
    What are the signs that a txv has gone bad?
    Nov 2001
    east kansas
    Overfeeding, starving, hunting.
    Tip: Save the cut sheet from TXV boxes. They have troubleshooting info and how to adjust them.
    Beware of advice given by some guy on the Internet.
    Apr 2004
    Bartlett, IL
    If I sell a job with a TXV, I sell the TXV cased coil.
    It's already installed.
    Apr 2005
    illinois
    Thanks for ypur reply but I do not know how hunting, overfeeding or starving manifest themselves. What would happen with these problems?
    Nov 2001
    east kansas
    Starving looks like the unit is short refrigerant, but your subcooling is mormal to high.
    Overfeeding your superheat is very low and compressor may be sweeting.
    Hunting is where your superheat never stabalizes.