Thread: door blower test- do I need it?

  1. #1
    Join Date
    Sep 2005
    Posts
    12
    Post Likes
    Since I now have had 3 different contractors over to give bids on replacing my 2- 20 yr. old systems ( a 3 ton & 4 ton)
    Not ONE offered to do a Manual J( even though it is required for the NJ state rebate) -Do you think I should have a door blower test done and what exactly does it show?
    Should I have an outside consultant come over and do the manual J and the door blower test-Since the house is 20 yrs. old- If so how do I go about finding such a person and how much approx. should it cost-Since we are going to be here a long time I want it done right- Everyone just asks are you comfortable now and then says just replace with the same size- Also a side question- The flex tubing from the handler to the ducts are starting to peel showing the insulation under it- 1 guy said you need to replace it and the others did not even mention it- Should I replace the flex tube or is it OK to have the insulation showing??- thanks for your help and sorry for the long post

  2. #2
    Join Date
    Oct 2005
    Posts
    68
    Post Likes

    Smile

    If it is required to do a manuall J load calculation then you need to find someone to do it. Another thing is just because you are comfortable now doesn't mean your system is sized correctly. I really recommend a load calc. and you also need to replace the flex pipe that is showing the insulation.

  3. #3
    Join Date
    Sep 2005
    Posts
    12
    Post Likes
    Thread Starter
    Thanks - Is a door blower test something I should also do?

  4. #4
    Join Date
    Oct 2005
    Posts
    68
    Post Likes
    I haven't ever heard of that type of test. That may be something required where you live. I am in Indiana and I have never heard of such a thing but definately do the load calc. and replace the flex.

  5. #5
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,835
    Post Likes
    It's an excellant thing to have done.It can show you the duct leakage and infiltration rate,they would normally recommend duct repairs and improvements to reduce infiltration,if either are high.

  6. #6
    Join Date
    Aug 2003
    Location
    Central Kentucky
    Posts
    6,258
    Post Likes
    A blower door is a great tool for diagnosing building envelope issues & infiltration rates, that is where it should stop though.

    I would not recommend it be used for duct leakage testing, it is a misapplication of the blower doors design intent.

    If you are interested in having your ductwork tested be sure the contractor you choose uses tools that are designed to actually measure airflow from HVAC systems.
    Have you set up a Google alert for Carbon Monoxide yet?
    Click here to find out how.

  7. #7
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,835
    Post Likes
    davidr,

    Blower door is commonly used by major utilites,etc. ,for duct leakage detection.Can you explain why you think it shouldn't be.


    I know ther are better ways,like http://www.aeroseal.com and duct blaster.but i think a blower door is fine.

  8. #8
    Join Date
    Aug 2003
    Location
    Central Kentucky
    Posts
    6,258
    Post Likes
    Originally posted by dash
    davidr,

    Blower door is commonly used by major utilites,etc. ,for duct leakage detection.Can you explain why you think it shouldn't be.

    For detecting leaks I have no issues, it is when they try to quantify leakage of CFM values with the blower door test.

    The utility companies around here do a blower door subtraction test & use this to deem wether duct systems are efficient, not doing their customers much of a service.

    Tight ducts are only one aspect of a properly designed system & have been focused on too heavily by the BS guys,I am preaching to the choir here though dash.

    I am going to throw in something else here,I also don't trust a duct blaster either.
    Have you set up a Google alert for Carbon Monoxide yet?
    Click here to find out how.

  9. #9
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,835
    Post Likes
    We find the dcut blaster to be accurate,what is it you have found.

  10. #10
    Join Date
    Aug 2003
    Location
    Central Kentucky
    Posts
    6,258
    Post Likes
    I am not personally big on the idea of using a fan that is foreign to the system to determine ductwork efficiency as some are using it.

    When it comes to using a fog machine combined with a duct blaster it can really show some interesting results, a great visual aid

    I am not putting these tools down, I am simply stating they should be used in the manner they were originally designed for.

    In what manner are you finding it accurate dash?
    Have you set up a Google alert for Carbon Monoxide yet?
    Click here to find out how.

  11. #11
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,835
    Post Likes
    We use the Aeroseal process,which is really a duct blaster with the ability to inject sealent.

    When the final cfm on leakage is determined ,after the sealing process,we find that testing with a flowhood ,and another dcublaster ,to leakage all comes out about the same. For the flowhood it's as compared to the TESP and the fan data sheet.

  12. #12
    Join Date
    Aug 2003
    Location
    Central Kentucky
    Posts
    6,258
    Post Likes
    That is something I find very interesting dash considering the way both test methods vary in how they are performed.

    Have you been using a fog machine with your duct blaster?
    Have you set up a Google alert for Carbon Monoxide yet?
    Click here to find out how.

  13. #13
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,835
    Post Likes
    No fog needed as we will use Aerosealto seal the leaks.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •