  1. #14
    Join Date
    Oct 2005
    Posts
    45
    So I am not getting any benefit out of having a 2 stage furnace?

  2. #15
    Join Date
    Mar 2004
    Posts
    1,042
    Originally posted by BaldLoonie
    Black, you can't do 2 stages of gas backing a heat pump with the VP. At least the way they have it designed. If you want to do some crazy wiring you might be able to jury rig something. I have an old Robertshaw 9720 and a DPDT relay. Pump is stage 1, gas backup is 2 & 3 though normally I have gas backup shut off via a toggle switch. A White-Rodgers 1F90 with 3 stage heat will do the same. The VP won't.
    Looks like Loonie's right- I just checked the VP manual. I hadn't thought about that issue.

    Blackadder, it looks like you *could* do (other than using the furnace board to control its own staging):
    -configure it for 2H/1C with your second heating stage as low fire, and emergency heat as high fire. About the same effect as a toggle switch, but tidy enough to not annoy the missuz.
    -use an outdoor thermostat to control furnace staging...?

    It's a shame it's so hard to get a single stage furnace with variable speed (Nordyne or bust?) A two stage furnace in conjunction with dual fuel is kinda redundant, and frequently control systems can't handle all the stages anyway. And just watch out if you're looking at a two stage heat pump and a two stage furnace... not much will handle that. Infinity systems can do it.

    Y'know, I just went looking, and apparently the Thermidistat can do four stages? I've never tried it, but it looks to me like they can handle a two stage heat pump with a two stage furnace. In fact they even let you program it to choose whether you want low fire or high fire for defrost tempering. It's not as pretty as a VisionPro, but in some ways I still like its bells and whistles better.

    And the regular Carrier dual fuel stat can certainly handle three stages in dual fuel, either with a two speed furnace or a two speed heat pump. I have to say, Carrier's dual fuel stat was way ahead of its time when it was released.

    [Edited by wyounger on 10-13-2005 at 02:24 PM]

  3. #16
    Join Date
    Oct 2004
    Posts
    40
    So if I have a HP with a two stage furnace with a VS motor I would be stuck with the HP and firststage heat only.

    The VP model I have has 3heat and 2 cool.

    Is it the VP that controls the 1st to second stage adjustment or is it the furnace?

  4. #17
    Join Date
    Apr 2004
    Posts
    7,680
    Originally posted by hamons
    So I am not getting any benefit out of having a 2 stage furnace?
    Yes you are. Not financial but comfort. The full fire is probably not needed. Mines a two stage furnace under a heat pump. Works great.

  5. #18
    Join Date
    May 2005
    Location
    Seabeck, WA
    Posts
    1,870
    BaldLoonie
    Associate

    Registered: May 2000
    Posts: 13299
    Black, you can't do 2 stages of gas backing a heat pump with the VP. At least the way they have it designed. If you want to do some crazy wiring you might be able to jury rig something. I have an old Robertshaw 9720 and a DPDT relay. Pump is stage 1, gas backup is 2 & 3 though normally I have gas backup shut off via a toggle switch. A White-Rodgers 1F90 with 3 stage heat will do the same. The VP won't.


    Yes you can. There are at least a couple of ways.
    With a trane you could just jump w1-w2 and there would be a 10 min timer for 2nd stage gas heat.
    I put in a Trane 16i (two stage) heat pump and did it with a vision pro. Use your imagination.
    Jason
    Live for yourself and ask no one to live for you.

  6. #19
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    6,272

    Thumbs up KC. VERY LOW $

    Originally posted by hamons
    I guess bottom line is I'll have to play with it. Lots of variables to mess with though.

    Setback temperatures and balance point.

    Right now balance point is set to 30 degrees.
    With those VERY LOW electric rate$,
    maximize heat pump use.
    28'F " seems " just about right.

    I didn't realize anyone is as low as $0.04/kW
    (except Time-of-Day rates).
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  7. #20
    Join Date
    Mar 2004
    Posts
    1,042
    That is really, really low. Is it really 4 cents total in KC? I know these things can be easy to misinterpret... utility rate structures can be absurdly complicated.

    I know if you go looking for Georgia Power's winter rate, it looks like 4.something cents per kwh, but if you read the fine print, their is a separate "fuel cost recovery schedule" that adds another 2.6 or so cents per kwh to cover the cost of the fuel for the plants. The four cents covers everything else.

  8. #21
    Join Date
    Oct 2005
    Posts
    45
    We get a special Heat rate if we use a heat pump.

    Standard Rate:

    Winter (8mos) = $.0651/kwh
    Summer (4mos) = $.0736/kwh

    plus monthly service charge of $5.78

    One Meter Electric rate

    Winter (8mos) = .0430/kwh for the 1000 kwh and .0339 after that

    plus monthly service charge of $5.76

    Summer = .0736

  9. #22
    Join Date
    Mar 2004
    Posts
    1,042
    Wow, wow, wow.

    I wouldn't let the gas company near my house if my electric rates were like that.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event