Originally posted by jcswaim
How can you tell or test a system to see if it short cycles?
The right size for an air conditioner is the size that will cool your home on a hot summer afternoon with only about 10 to 15% Btu/hr to spare. When we install more air conditioning Btu/hr than this, it will, especially under part-load conditions, do what we call "short cycling."
It only runs for a few minutes--maybe five or ten at a time--and then shuts down for a few minutes, before starting up again. In these short cycles it cools the house, but it does a very poor job of removing humidity. it also takes around five minutes on each start-up to get to full capacity cooling! This will greatly lower the operating SEER rating of your equipment, therefore the recommendation of the wide temp differential room TH.
Most room TH's used to have a cooling anticipator that actually caused the unit to keep the room temperature within a very tight differential, --leading to a worst possible short-cycle scenario!
Therefore, decide what you want, a close temp differential or a wider differential with a longer run-time and less on/off cycling for more efficient operating performance! Darrell
Will it short cycle when it heats the home as well?
Haven't had a chance to take any pics yet, but I have been monitoring the time it comes on and shuts off. So far it has come on twice in one hour. I have it set on 75 and it is 78 outside. Does this sound ok?
That's not short cycling, if that's what you mean.
...seek, and ye shall find;.. So always seek the Truth, not just what you want to believe to be true… Ecclesiastes 10:2 NIV
Oh NO
Once again someone replaces a 20++ year old 3-Ton system with a 4-Ton System. Because “Bigger is Better”.
As far as ratings between units make sure you are comparing apples to apples. Some manufactures (TRANE) don’t include the heat produced by the blower. I’m not sure if Goodman includes this in their ratings.