Results 1 to 10 of 10
Thread: Sizing question
-
10-11-2005, 02:04 AM #1
Regular Guest
- Join Date
- Aug 2004
- Posts
- 91
If I have a furnace sized for the coldest day of the year, it will be oversized for the majority of the year. ie: We have maybe 10 days/year at 30F but most winter days are closer to 45F. So, would your design temp be 30, 45 or somewhere between the two?
-
10-11-2005, 05:56 AM #2
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,271
LOCATION ?
Design Temp may be about 35'F.Originally posted by martik
... have maybe 10 days/year at 30F but most winter days are closer to 45F.
Location ?
A.S.H.R.A.E. data and statistical ( < 1 or 2% of time) procedure determines the Design Temperatures
Other furnace sizing factors:
LOCATION
House SIZE
Number of stories
House Age
Insulation values: ceiling, wall & floor
Window sizes, orientation and U-value
Infiltration
Efficiency: output capacity versus actual heating delivered
Aside: Current size furnace
Perform ACCA Manual J calc or provide additional details so that reasonable "ball-park" guidance may be provided.
USE "HVAC Calc" available on right side of tab above.
OR see you local HVAC PRO if you will be buying
a new furnace soon.Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
10-11-2005, 08:36 AM #3
Regular Guest
- Join Date
- Nov 2002
- Location
- VA
- Posts
- 296
Have you considered a Heat Pump?
martik
With winter extremes so mild, I'm have to assume at your summer extremes are high. Are you in a humid climate (A.K.A. green grass)? Either way sizing for your cooling load may drive the equation for the air handling system. However without qualifying location no meaningful answers can be given.
That said, it might be to your decided advantage to consider a Heat Pump instead of a fossil fuel heating source. They are at their best in the temperature range you're indicating. Given the current fuel prices electrical may have a decided long-term advantage since it isn't exclusively dependent upon somewhat questionable sources and depleting national reserves.
Please Note: Im not pro/con either way on equipment fuel type. In fact natural gas furnaces have a decidedly longer design life (tried, true and proven) than refrigeration equipment. Its just that the realities of fossil fuel have changed over time and we all need to consider the finite nature of that resource.
Sometimes speaking with local contractors who deal with your issues on a professional basis has much merit. Ask each of them to explain their recommendations in terms of initial investment and operating cost verses comfort provided...
God Bless...
-
10-11-2005, 04:31 PM #4
Regular Guest
- Join Date
- Aug 2004
- Posts
- 91
Thanks for the replies.
I am aware of the factors involved in a heat loss calc. I was just curious how you determined the design temps and it appears you don't base it on the LOWEST temp of the winter.
My contractor advised that a heat pump does not last long enough to justify the savings.
Gas has already increased 20% this year and probably will continue to rise so I have considered Zone heating with baseboard heaters. Electricity is only 6cents/KWH here.
-
10-11-2005, 04:35 PM #5
Ask for several opinions. One contractors opinion isn't gospel. Here in ATL heat pumps work great when designed and installed correctly in conjunction with a secondary fuel.
-
10-11-2005, 05:22 PM #6
Design temp is from manual J.
Give your area, and we can look it up for you.
If you size for 45°, the 10 days that its 30° out, your house will be 55 inside.
Your contractor may not like heat pumps.
But if they were as bad as he says, no one would use them.
-
10-11-2005, 07:21 PM #7
Regular Guest
- Join Date
- Aug 2004
- Posts
- 91
Vancouver BC, Canada
Another question: If a 100k btu furnace runs approx 1 min on, 3 mins off during an average winter day could one
assume it is oversized by 300%?
-
10-12-2005, 04:55 AM #8
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,271
Load Calc
80,000 BTUh Output ?Originally posted by martik
Vancouver BC, Canada
Another question: If a 100k btu furnace runs approx 1 min on, 3 mins off during an average winter day could one
assume it is oversized by 300%?
Night time operation ?
It might be 20% to 50% oversized.
50,000 to 70,000 BTUh might be in the ball park.
Also, the T-stat may not be working properly.
You need to look into an Efficient heat pump
to save lots of $$$$
based on those LOW electric rates.
Buy 10-year warranty on Parts & Labor for a few hundred $.
Sounds like your house is 1,600 + square feet.
TRANE model 2TWX4042 might be about right ...
__ Windows u-value and areas are needed.
However, a SPECIFIC ACCA Manual J (or other)
load calc is Required.
[Edited by dan sw fl on 10-12-2005 at 05:28 AM]Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
10-12-2005, 05:29 AM #9
97 1/2% design winter is 19° summer 77
-
10-13-2005, 12:15 AM #10
Regular Guest
- Join Date
- Jul 2004
- Location
- Kent, WA
- Posts
- 129
I was surprised by that number, but you're right. Here in Seattle, our weather is very similar, but the design temp is 26° F, seven degrees higher. Must really get cold on those few times it gets cold.