With the technology today, and for best product temp control, its a simple solution. Thermostat, solenoid, and defrost clock. Defrosts are totally dependent on climate, but 4 times a day, at 45 minutes apiece will ensure a 100 percent clear coil, but not warm up enough that the customer will notice. If anyone asks you to anything different, they are cutting corners, and trying to save money on the install. If you're not going to do it properly on the install, don't bother. You seem like you have the right attitude. Keep up the good work, and don't listen to the guys wanting to save the customer $10, and cutting corners.
-
09-19-2012, 12:05 AM #28
-
09-19-2012, 03:40 PM #29
Professional Member
- Join Date
- Dec 2004
- Posts
- 484
Did not read through entire thread so my apologies if this has been covered. I always prefer controlling temp with a lpc for a few reasons.
1. Offers compressor protection
2. Kiss timeclock can't fail if it's not there
3. Customers can crank stat down but I control how low it will go
4. Saves nuisance calls from iced up coils due to door being left open or fans turned off because it's self regulated.
5. Maintains better product integrity
6. Better energy efficiency
7. Compressor life extended because it cycles better
Sidenote regarding blends
They are a bit trickier what you need to member is that they enter as a liquid and exit as a vapor and only in the center are they a true saturated state.
For example say you are looking for a co evaporation temp of 15degrees and your refrigerant has a corresponding bubble point of 10lbs and a dew point of 20lbs the correct co pressure is 15lbs.
What that does is compensates for the glide and should produce 15 degrees at the center point in your coil. It sounds more confusing then it is but it does work.
-
09-29-2012, 07:47 AM #30
Professional Member
- Join Date
- Jul 2011
- Location
- Lehigh Valley, PA
- Posts
- 224
Johnson Controls A419 works well. Solved two different icing issues without timers. Both older systems with high user activity.
-
09-29-2012, 09:28 AM #31
-
09-29-2012, 09:36 AM #32
-
09-29-2012, 08:17 PM #33
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
-
09-30-2012, 12:45 PM #34
JP turned me on to the Ranco A12-1506. It has worked very well on two occasions where there was a control failure.
[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
-
10-01-2012, 08:42 AM #35
I started reading this thread this morning till I got to my original posts. Then I realized this was from 2005, LOL. Anyways, I actually quit using this setup. I don't know why. Maybe at the time I was working for someone, and now I'm a owner. I do remember I had good results at the time. Mostly used it on walk in beer coolers. Nowadays, I just add a defrost timer, four defrosts a day, air defrost for 45 minutes.
I use the Ranco A12-701 (constant cut in @41) for reach in coolers.
-
10-01-2012, 08:42 AM #36
Double post
-
10-01-2012, 11:32 AM #37
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
-
10-02-2012, 09:08 PM #38
Here is a Ranco page that shows how the controls compare for temperature range.
http://www.uni-line.com/images/docs/...erence-pg3.jpg[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
-
10-03-2012, 03:38 PM #39
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410


Reply With Quote
Does it do anything special ?