    if your suction side gauge pressure is low what could be the problems besides low frion

  2. #2
    Join Date
    Oct 2005
    Location
    Tempe, Az
    Posts
    7
    Post Likes
    No fan, dirty air filter

  3. #3
    Join Date
    Sep 2004
    Location
    Memphis
    Posts
    2,502
    Post Likes
    possibly a restriction in the metering device.
    Life is like a jar of jalapenos. What you do today might burn your ass tomorrow.

  4. #4
    Join Date
    Mar 2004
    Location
    SE Michigan
    Posts
    19,029
    Post Likes
    Low on gas, restricted exp. valve, restricted drier, low ambient temp. causing low head pressure...
    To put the world in order, we must first put the nation in order; to put the nation in order, we must put the family in order; to put the family in order, we must cultivate our personal life; and to cultivate our personal life, we must first set our hearts right.
    -- Confucius

  5. #5
    Join Date
    Jul 2001
    Posts
    3,112
    Post Likes
    gage out of adjustment

  6. #6
    Join Date
    Apr 2005
    Posts
    18
    Post Likes
    weak compressor valves....

  7. #7
    Join Date
    Oct 2005
    Location
    Georgia
    Posts
    5
    Post Likes
    What is your head pressure and outside temperature?

  8. #8
    Join Date
    Feb 2005
    Location
    Dothan, Al
    Posts
    3,453
    Post Likes

    blikmik

    As simply as I can put it.
    a) low refrigerant flow into evaporatot.
    1) low refrigerant level
    2) restriction causing low refrigerant flow

    b) low air flow
    1) filter stopped up
    2) indoor coil stopped up
    3) Blower motor not running ( or not running at
    correct speed )
    4) Can't pull enough return air ( ductwork )
    5) can't push enough supply air ( ductwork )
    6) Return air bypasssing coil

    c) low indoor ambient temp:
    may also be helped by low outdoor ambient at same
    time.