Daikin VRV Integration
I am integrating to a Daikin system and was able to successfully connect to the D-BACS gateway and program the IP address and the device instance, but cannot see any of the units when I click "Operating State". Also not able to autodiscover any of them. All units are powered on and wiring is solid, but I get nothing. Is there some crucial step that I missed? It seems like it's probably just something silly.
-
07-01-2011, 06:06 PM #2
What system are you integrating to?
I have most of the manuals for this integration, but it would help to know what you are integrating the Daikin to? (Carrier, ALC, Honeywell, JCI, etc..)
Are you using a third party point sniffer like BACnet Explorer?"We are what we repeatedly do. Excellence, then, is not an act, but a habit" Aristotle
Remember to "Pay it Forward"; help out the newer generation of techs, remember someone during our career helped us! ("Pay it Forward" was by someone smarter than me!!)
-
07-01-2011, 06:10 PM #3
Missed the attachment
Sorry first post didn't catch attachment
"We are what we repeatedly do. Excellence, then, is not an act, but a habit" Aristotle
Remember to "Pay it Forward"; help out the newer generation of techs, remember someone during our career helped us! ("Pay it Forward" was by someone smarter than me!!)
-
07-01-2011, 10:08 PM #4
Permanently Removed
- Join Date
- May 2002
- Posts
- 9,564
This is a side point - but I like it that the Army Corps of Engineers disallows these type of control systems. There is no reason why it needs to be a separate proprietary communication.
-
07-02-2011, 02:31 AM #5
Regular Guest
- Join Date
- Jun 2011
- Posts
- 9
-
07-02-2011, 11:12 AM #6"If you can't explain it simply, you don't understand it well enough
Albert Einstein
"Don't you just love when the flames burn off the wiring schematic?" hvacvegas-HTALK member
-
07-02-2011, 11:29 AM #7
Regular Guest
- Join Date
- Jun 2011
- Posts
- 9
-
07-05-2011, 09:22 AM #8
Regular Guest
- Join Date
- Jun 2011
- Posts
- 9
-
07-05-2011, 05:26 PM #9
Regular Guest
- Join Date
- Feb 2010
- Posts
- 28
Have each of the indoor units been assigned a group address? If not, do that and then cycle power on the gateway.
Pres
-
07-06-2011, 11:57 AM #10
Regular Guest
- Join Date
- Jun 2011
- Posts
- 9
-
07-14-2011, 11:51 AM #11
Regular Guest
- Join Date
- Jun 2011
- Posts
- 9
bump for the daikin experts
-
07-14-2011, 12:33 PM #12guitarman25 Guest
Some notes from our Daikin experience, which involved fan coils and condensers:
Com wire is very sensitive. Shielded wire was mistakenly installed at a few units and did not work at all. When replaced with no-shield, it worked.
If landing 2 wires under a terminal, do not twist them together. Sounds strange, but made a difference.
Make sure all units are the same (i.e.VR3, VR2, etc.) The manufacturer sent some of the wrong model, and they of course would not communicate.
Power the master first, then add the slaves.
Double check the terminals F1 and F2, Q1 and Q2 from unit to unit.
It seemed that if one thing was wrong, we could not see the entire system, so start at the very first unit, disconnect from the rest, and work your way down.
Good Luck!
-
10-05-2012, 02:28 AM #13
New Guest
- Join Date
- Oct 2012
- Posts
- 3
hi xarralu. what software is this from AutomatedLogic?