Results 1 to 9 of 9
    Geothermal and Backup heat
    Do most geothermal heat pump systems get installed with some kind of backup heat?
    What are the pro's and cons to sizing a geo heat pump so that you don't need backup heat?
    Jul 2010
    jeff I don't know the % that have backup heat. I had it put in mine and when I saw how good the system worked I disconnected it. So for me it was a waste of money. The idea is to size your system for 9o to 95% of your heat need and the 5 to 10% that you might need every 3 or 4 years can be made up with backup that could save you several thousand dollars in the install. To me the big problem is that if you have a problem with your system You want know it until you get your power bill as the backup would make up the heat loss for say low freon. If it happens slowly you would get used to the higher power bills and never know that you had a problem. Also it is hard to burn down your house if you don't have any fireworks in your system. That's just my 2 cents. You will love Geothermal. Curtis
    Lynchburg, VA
    Thumbs up
    I routinely size the 2 stage geo systems so the first stage operation will handle most all the cooling and heating load with the second stage rarely being used. I will also configure the t'stat so there is no auxillary heat available, the t'stat would have to be manually set to "Emergency" heat in the event of a system shut down.
    This allows for maximum energy/cost savings which is the very reason the homeowner has invested in such a system. I also size the loop field with an additional 20% capacity to allow the system to always work at it's maximum efficiency. I never want to receive a phone call from the customer saying the geo system is not performing as intended.
    Mar 2011
    East Coast FL
    Maybe an electric duct heater in case you loose the pump?
    In a boiler room
    I agree with post 2. Size system to handle 95% of design "coldest day of the year" conditions. You will save money on the install and auxiliary heat will be used on average about 1-4 hours per year.
    I turn off my emergency and auxillary heat breakers and only use them when necessary. My compressor went last year and I was able to heat with my backup.
    Sep 2009
    I'm installing a 5 and a 3 Tom Geo in a house and it's 7000 Sq ft. 3500 on main and 3500 in basement. I sized for the house to be 75 at 0 outside on heating and 70 when it's 100 on cooling. Allot depends on how your house is built. I also done a max water temp in summer or 95 and min winter of 35. This makes my loop longer to accept and reject heat. Soil matters too. I'm not installing backup cause it's not need until -3. And the homeowner oppt out of it. You can always install later. I don't see no cons to it. The pros are if your compressor goes out, you still have heat.
    Dec 2011
    If you over size the heat pump you are going to be paying for a system larger than you need for 95% of the time. During the cooling season with an over sized system it will cool the house too quickly and not remove the humidity so it will feel calmy.
    Aug 2011
    Northwest Indiana
    In our climate we have a greater heating load than cooling so I size a 2 stage unit for 95% of the heating load and provide some form of auxiliary or backup heat - either gas furnace or electric strip heat. A 2 stage unit allows for the 1st stage to nicely cover the cooling load without being grossly oversized. A single stage unit in my climate would be either (1) on backup all the time in heating or (2) cool very poorly (as in not be comfortable - you could probably hang meat in a house with a grossly oversized AC)