10-29-2005, 01:29 AM #14
Professional Member*
- Join Date
- Sep 2001
- Location
- Vancouver Canada
- Posts
- 996
Does the heatpump cut out completly when the furnace comes on? It is definetly not recommended to run furnace and heatpump at the same time. That is the purpose of a fossil fuel kit or outdoor temp stat on Vision Pro tstat. The Hpump MUST be turned off before the furnace comes on. You can set any differential you want but I would turn the gas off to the furnace until this situation is rectified. Other wise you may find yourself shopping for a new heat pump.
"Go big or Go Home"
-
10-29-2005, 09:24 AM #15
Regular Guest
- Join Date
- Jun 2005
- Posts
- 44
Yes--thermostat is set for add-on heat, locks out compressor when calling for aux heat/second stage.