    AAON Dehum question

    I recently came across a Aaon RTU 6ton I believe R-22. This RTU controls a testing room for a car part supplier. They are trying to control 45-55% rh in this space. Lately the humidity has been creeping up and the dehum mode doesn't seem to be keeping up. Any suggestions? I did notice that the dehum is activated and the first stage compressor is running with the cfm. Also the first stage has hot gas bypass. I'm not sure if I'm just having a brain fart or I am overlooking something. The space temp has been steady between 70-72. But the humidity is my problem. Any help would be appreciated.

  2. #2
    Join Date
    Apr 2010
    Location
    Minnesota
    Posts
    536
    Post Likes
    I can't speak specifically of AAon, but I worked on a new Trane 8.5 ton plenum fan style RTU with dehum. It's logic runs both stages of cooling, and energizes a 4 way valve for reheat on a call for dehum. The reheat coil is connected only to 1st stage compressor. There's no way to run only 1st stage comp during dehum on that unit. Even with both stages running it yields a 4* delta t. Hope this info helps some. Maybe your 2nd stage only starts when the temp rises enough in the space to call for cooling? Have you checked the charge? Make sure your hot gas bypass isn't messing you up. I;m guessing that should only be active during low ambient conditions.

  3. #3
    Join Date
    Apr 2010
    Location
    southern california
    Posts
    535
    Post Likes
    Quote Originally Posted by dmd-marc View Post
    I recently came across a Aaon RTU 6ton I believe R-22. This RTU controls a testing room for a car part supplier. They are trying to control 45-55% rh in this space. Lately the humidity has been creeping up and the dehum mode doesn't seem to be keeping up. Any suggestions? I did notice that the dehum is activated and the first stage compressor is running with the cfm. Also the first stage has hot gas bypass. I'm not sure if I'm just having a brain fart or I am overlooking something. The space temp has been steady between 70-72. But the humidity is my problem. Any help would be appreciated.
    Is it a safe assumption that this unit has worked correctly for several years. If the answer is yes then there is either a problem with the controls, or refrigerant charge, or something has changed in the room which is adding more humidity to the space. Post the model number of the unit.

  4. #4
    Join Date
    Jan 2011
    Location
    WI
    Posts
    81
    Post Likes
    Aaon has a mess of controller's out there. Post a model number of the unit, and try to get a model of the controller.

  5. #5
    Join Date
    May 2004
    Location
    new jersey
    Posts
    338
    Post Likes
    Quote Originally Posted by acwizard View Post
    Is it a safe assumption that this unit has worked correctly for several years. If the answer is yes then there is either a problem with the controls, or refrigerant charge, or something has changed in the room which is adding more humidity to the space. Post the model number of the unit.
    agreed if the unit has been working i would start looking at ref charge.
    is there bldg automation co controlling it or is it wattmaster

  6. #6
    Join Date
    Feb 2011
    Location
    richmond, va
    Posts
    29
    Post Likes
    need more info, does this unit have a reheat coil, do you have a mhgrv board that controls your stepper motor

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •