    Surge

    I have a Carrier Chiller 19XL, making surge,the gpm in evaporator and condenser are ok, please let me know what to do, the surge begin when the load is increasing

  2. #2
    Join Date
    Jun 2010
    Location
    U.A. (upper Alabama)
    Posts
    788
    What's the approach temperature on each?

  3. #3
    Join Date
    Jan 2011
    Location
    Puerto Rico
    Posts
    14

    Approach

    The approach in both condenser and evaporator are in 2 degrees F.

  4. #4
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    992
    what are your pressure and temps on the condenser., seems to be fine at low temps, but when the machine loads up u have problems, the 2* approach , i would think that would elimate air, i would check tower water and tubes.
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

  5. #5
    Join Date
    Jun 2010
    Location
    Tampa, FL
    Posts
    101
    R-22 chiller. Non condensibles? Unlikely but check anyhow. Could be a sensor problem. Veryfy sensor readings. Surging high or low? Check refrig level. Make sure water is not bypassing at cond divider plate. Measure dp at end opposite piping.

  6. #6
    Join Date
    Jan 2005
    Location
    Houston TX
    Posts
    868

    Give us the information, please

    Aleyara- I'm sorry but everybody who is trying to help you will need a lot more information then just 2*F approach on condenser and evaporator. Start with a complete model #, the number of condenser and evaporator passes, Condensing pressure and temperature, Evaporator pressure and temperature, Water temperature entering and leaving both vessels. In other words a complete log of actual operating conditions, as is when It starts to surge. The number of passes for a 19XL can be as many as 4 on the evaporator, I believe, but not sure. A 2*F approach sounds a little close to carry over. While your compiling your data also take a reading of your discharge gas temperature. If you have a pic-II controller you may have to measure actual temps and pressures as compared to the readings on the screen. One other thing that would help you cause would be to locate the original design date from Carrier. Talk to you later. -GEO
    Once in a while everything falls into place and I am able to move forward, most of the time it just falls all over the place and I can't go anywhere-GEO