  1. #1
    Join Date
    Sep 2005
    Location
    Ontario
    Posts
    19

    Hmm

    Are there any special precautions or requests that I should be aware of if/when my contractor installs an A/C system in cold weather?

    I have read that the charging of the A/C system becomes more complex since the amount of installed r410a requires adjustment.

    Is this a routine adjustment based on the temperatures and volumes of the inside and outside components?
    Should I request that the system be re-checked in warm weather?

    My r410a system has not been purchased yet.
    I am asking this forum in case there are requests that I could/should add to my contract.

    Thanks

  2. #2
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,743
    not that it HAS to be done but we always go back in the spring and check our winter installs.

  3. #3
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    34,184
    Exactly. High SEER requires perfect refrigerant level and that can't be done in cold weather. Needs warm outdoor temps and a load inside.

  4. #4
    Join Date
    Mar 2003
    Location
    PA/DE area
    Posts
    1,535
    We install and set date before we leave with homeowner and service dept,then mail post card to remind them!!!!
    It's NOT the BRAND,it's the company that installs it!!!!!

  5. #5
    Join Date
    Sep 2005
    Location
    Ontario
    Posts
    19

    Wink

    posted by BaldLoonie
    Exactly. High SEER requires perfect refrigerant level and that can't be done in cold weather. Needs warm outdoor temps and a load inside.
    Thanks for all the feedback.
    What is your definition of "cold" and "warm" weather for the above?

    I've have now removed myself from the buyers frey with the purchase of a furnace & ac system. My contract states that a pressure re-check will take place in the spring if it was "too cold" at the time of the installation.
    I'm kicking myself now that I did not define "too cold" before hand. The one point of reference that I have is the product data which states not to operate the A/C below 55F.

    Dont tell me that 55-70F is a grey area. :-)

    I assume that inside load is just a matter of dropping the tstat.

  6. #6
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,743
    i like it to be at least 65-70 and dry out.

  7. #7
    Join Date
    Sep 2001
    Location
    Vancouver Canada
    Posts
    996
    Prefer minimum of 70 outdoors with a bit of load indoors
    "Go big or Go Home"

  8. #8
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    6,295

    Smile Satisfaction Guarantee

    Originally posted by eeh
    posted by BaldLoonie
    High SEER requires perfect refrigerant level and that can't be done in cold weather. Needs warm outdoor temps and a load inside.
    My contract states that a pressure re-check will take place in the spring if it was "too cold" at the time of the installation.

    ___ I did not define "too cold" before hand.
    "Too Cold"
    _________ Outside T < Inside T ( i.e. 74')

    All Reasonable mechanical contractors will work
    with you on this one.

    It is not a difficult job to adjust refrigerant level in late spring on a newly installed system and assure your satisfaction.
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event