    3 phase motor winding resistance

    i was looking at an airhandler today at a powerplant that was tripping the breaker. After jumping through all the hoops to get the clearance to work on the thing. i started checking for shorts. i found the fuse block for the 3 phase blower motor burnt up. I went to check the windings of the motor to see if they were grounded and they were not. but i was getting 2.4 ohms across all the windings in the motor. if ohms law is correct and i have a 460 volt motor rated at 6.2 amps should i be reading 74.19 ohms? if so then would it be safe to say the windings are shorted? i feel like this is a dumb question and i shouuld know this by now but i just cant get this through my head today.

  2. #2
    Join Date
    Jun 2006
    Location
    New Jersey
    Posts
    4,456
    Post Likes
    Quote Originally Posted by mjm88 View Post
    i was looking at an airhandler today at a powerplant that was tripping the breaker. After jumping through all the hoops to get the clearance to work on the thing. i started checking for shorts. i found the fuse block for the 3 phase blower motor burnt up. I went to check the windings of the motor to see if they were grounded and they were not. but i was getting 2.4 ohms across all the windings in the motor. if ohms law is correct and i have a 460 volt motor rated at 6.2 amps should i be reading 74.19 ohms? if so then would it be safe to say the windings are shorted? i feel like this is a dumb question and i shouuld know this by now but i just cant get this through my head today.
    Ohms law doesn't work for induction. You would need to know PF.

  3. #3
    Join Date
    Feb 2009
    Posts
    115
    Post Likes
    Thread Starter
    power factor is 86.5

  4. #4
    Join Date
    Dec 2010
    Location
    georgia
    Posts
    95
    Post Likes
    2.4 ohms sounds right for that size motor.

  5. #5
    Join Date
    Mar 2010
    Posts
    32
    Post Likes
    just do a normal check of system you might want to meg wires back to mcc panel. check incoming power at your starter, check your contacts, voltage drop across etc. but burned fuse block sounds like loose connections.assuming heaters,fuses,wire gauge are all sized right. then fire the unit up and take a current draw, see what you got and go from their.

  6. #6
    Join Date
    Apr 2005
    Location
    where the beer flows like wine
    Posts
    2,869
    Post Likes
    the ohms reading are right, you need a megger and test the windings to ground.

  7. #7
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by mjm88 View Post
    power factor is 86.5
    I think you are looking at efficiency, and not power factor.

    Power factor is a value between 0 and 1, and is a ratio of active power (in watts) divided by apparent power (in volt-amperes). A purely resistive load has a power factor of 1, or "unity." Motors are a combination of resistance AND induction. When you have induction, you have a counter-force that opposes current flow in the windings of the inductor.

    An ohms law calculation based on winding resistance and rated amps is meaningless, because counter EMF will limit current in the windings just as effectively as a higher resistance would do.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  8. #8
    Join Date
    Feb 2009
    Posts
    115
    Post Likes
    Thread Starter
    hey guys i appreciate the help! i got it going this morning. the fuse block was burnt up because of coal dust shorting between phases. replaced fuse block and fuses and she took off. put on a new belt and amped it out and all is well. i was just confused and a little intimidated by the size of the equipment. and not being able to bring power back to the system very easily without signing on and off clearances and all that good stuff that just takes lots of time

  9. #9
    Join Date
    Oct 2010
    Location
    Waco Texas
    Posts
    116
    Post Likes
    I work at a power plant also. The saftey cleances take a lot of time but its billable time and there for cya and your safety now the mines are a different story MSHA regulations are just laughable. My first day at the power plant the "tech" and I were replacing a compressor HE condemed. I ohlmed the winding found that they were good. He said they were weak since they were equal also he said he had put a HARD START kit on it and It wouldnt work a few days before. I dont how he become a techncian the unit has a 3 phase compressor. Im still waiting to see the ladder schmatic for that lol.

  10. #10
    Join Date
    Feb 2009
    Posts
    115
    Post Likes
    Thread Starter
    i've been working there for a couple weeks now. taking over for another tech that was working there. its just frustrating not being able to turn power on and off as you please. especially when you have a short somewhere.

  11. #11
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by mjm88 View Post
    hey guys i appreciate the help! i got it going this morning. the fuse block was burnt up because of coal dust shorting between phases. replaced fuse block and fuses and she took off. put on a new belt and amped it out and all is well. i was just confused and a little intimidated by the size of the equipment. and not being able to bring power back to the system very easily without signing on and off clearances and all that good stuff that just takes lots of time
    Coal dust? Wow.

    Hope you wear a mask!
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  12. #12
    Join Date
    Oct 2001
    Posts
    6,966
    Post Likes
    if the area was humid or dust on the windinds might of read shorted....all 3 should read the same between or to ground.where the covers on the contactors closure arc will trip the breakers as the arcs catch each other mean while your looking at the load....check the contactors for shorts between the L1,2,3 and T 1,2,3 sides and to ground.i.ve read fuses in humid mechanical rooms closed on a digital meter gone out into the street and the fuse is blown(open)...
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY

  13. #13
    Join Date
    Feb 2011
    Location
    OH
    Posts
    150
    Post Likes
    i think that is a smoken gun woe.

  14. #14
    Join Date
    Oct 2001
    Posts
    6,966
    Post Likes
    if the area was humid or dust on the windinds might of read shorted....all 3 should read the same between or to ground.where the covers on the contactors closure arc will trip the breakers as the arcs catch each other mean while your looking at the load....check the contactors for shorts between the L1,2,3 and T 1,2,3 sides and to ground.i.ve read fuses in humid mechanical rooms closed on a digital meter gone out into the street and the fuse is blown(open)...
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY

  15. #15
    Join Date
    Dec 2008
    Location
    caribbean
    Posts
    78
    Post Likes
    Is it a chilled water AHU?

    Few week ago I went to a service called, I found one of the fuse blown, the costumer told me that it wasn't the first time this happened,

    The issue had been happening almost FOR a year, anyway a long story short the chilled water valve was wired wrong. It was a N.O valve so every night once the fan stopped by schedule or system reached set-point the chilled water kept flowing through the coil so the blower motor was sweating like crazy!! I End up installing a aux relay to be able to close it after every time that reach set point.

  16. #16
    Join Date
    Jun 2011
    Location
    Baltimore,MD
    Posts
    8
    Post Likes
    Other things to note in large industrial plants is that they don't always use WYE transformers alot of cases they use a Delta/Center leg ground transformer. L1 and L3 will have the motors thermal overloads which will open and save the motor so if L2 was the ground it could have blown the fuses.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •