ceiling mounted climatemaster geothermal heat pump, i need help
i got a government building that has just recently installed 47 ceiling mounted geothermal heat pumps. they are all climatemasters. i am having a problem with a handful of units that are going into a lockout alarm. pressures are good, they run for a period of time (some run a few hrs and some run for a couple days) and when they lockout the fan continues to run. condensate is clear, freeze protection checks out. i am about to change out the control board on 1 unit. anyone got any experience with these climatemasters, have you had this problem and what you did to fix it?
-
07-11-2011, 03:04 PM #2
Regular Guest
- Join Date
- Nov 2007
- Location
- Central Alabama
- Posts
- 34
Model numbers would be nice information to have. What code is it giving you?
-
07-11-2011, 04:51 PM #3
Sounds like water flow problem. Have you checked screens on these units?
Always seems like there is dirt in lines no matter how much flushing is done.5 out of 4 people don't understand fractions
-
07-19-2011, 12:34 AM #4
Do they have flow restrictors?How high is your water level in the tower sump
-
08-07-2011, 10:38 PM #5
I also would check your y strainers screens
-
12-15-2012, 10:03 AM #6
Dirt,dirt,dirt......in other words water flow. Also water temperature. Check that beafore you start replacing control boards.