    I use 2 wire ties....one around the bracket that is very loose, and the second around the wires and looped through the first wire tie.
  2. #28
    Dec 2009
    Hotlanta GA.
    And so now, the picture is starting to clear up a little.
    Good point on delta across coil, we will see on a regular day temperature of 95, the entering air could be from 95 to 115 depending on were you are standing along the side of the unit between the two running. YES, there is definetly an air circulation issue. Anyoine want to take a stab at fixing it !!!!
    picture three RTAC 500's side by side with 12 feet between them, mostly open area around them.
    As for the oil temp. I understand the safety shut down, very well done. Now move me along into the load and unload of the female valve ????? I am recalling reading that valve was a 30% step after start up ?? Book not in front of me, so be polite about my memory !!
    Keep it comin, and yes I can use probes to take temp readings, will mor then likly use a mop handle with a thermister taped to the end. May need an exstention thermister cord !!
  3. #29
    Aug 2009
    Prattville, Alabama
    It's impossible to over-stress the importance of verifying all condenser fans are running when they should. The only way to do it is climb up there and feel the air flow off each fan. Don't just walk it while looking down- feel it and make sure you're not feeling reverse flow. I have seen others make this mistake several times. Your mop handle with a short piece of string or ribbon may work, but you won't be able to also inspect the fan wiring this way. I think a combination of these two methods would be OK. I have 2 RTAC200's on my building's roof, about 100 feet apart, in Montgomery, AL. I've seen head pressure of about 210 psig at full load on a 95 degree day. Any hotter, both chillers are running.
  4. #30
    MEXICO
    the problem of high oil temperature and / or high pressure in a machine I had in Cancun, but was due to a high level of oil.
  5. #31
    ottawa canada
    Quote Originally Posted by servicetrane View Post
    Good point .But if the charges of refrigerant and oil havent been monkeyed with my money is on the combination of dirty coils , wrong rotation and or non rotation of fans and air recirculation problems .
    But if the history of the chillers is full of recharge and or oil issues etc etc . then it could be oil/refrigerant/noncondensibles etc .
  6. #32
    Jun 2010
    Tampa, FL
    I worked a startup on one of the first RTACs in our area central FL. It had very high head. After exhausting everything I knew and coming up empty I called tech support. Should have called first. They knew they had a problem. After sending data file and mod and sn conversation went something like this. Did you check the oil level on the separator. Yes is within the factory specified limits. OK do this remove oil until it is below min oil level. You can always add more. I removed over 5 gal oil before machine settled down. Apparently oil overcharge blows on through separator and trashes heat transfer on condenser from refrigerant side. Maybe it was just an isolated incident with new product etc,etc. If you have access to software level that you can graph and analyze operating conditions it will go a long way to understanding the problem. Otherwise call Trane. Could be a warranty issue or will be when you start loosing compressors.
  7. #33
    Mar 2011
    Quote Originally Posted by Mongo and me View Post
    And its not Delta T, here in Atlanta its AIR TRAN T !!!! LOL..........
    I thought it was DIXIE-T!
  8. #34
    Mar 2011
    The machines are spaced 10 feet between each at set of three each, so two sets of three, the three are seperated 10 feet, the sets are over 100 feet between. all are sitting on pads on the ground. no reall wall toubles. Today you could walk down between the two running side by side and see 110 air being sucked in........ Yep there may be a recirculation problem !!!!
    We had (4) 400 ton RTAC chillers side by side, surrounded by a wall, and covered by a steel grate overhead. We suspected an air re-circulation problem. We used smoke bombs to visualize the airflow and confirmed re-circulation.
    The customer added ducts on top of the fan deck to direct the discharge air up higher to get it away from the coils.
  9. #35
    Dec 2009
    Hotlanta GA.
    Smaoke bombs I LIKE that !!!
  10. #36
    Dec 2009
    Hotlanta GA.
    Hey "The Chiller Man", were did you place your smoke at, we did a simular test here and the smoke went in and up out the fans, I balieve they set them on the ground. I balieve it would be better to set them on the outer edge of the machine, up by the fans.
    Also all, if ya bypass the VFD will the unit still bring in the relay and run the "A" fans......with out repograming ....
    Also, we have those new interface pannels, touch screen, small ones, is it possible to reprogram at the screen with out a lap top ????
  11. #37
    Dec 2009
    Hotlanta GA.
    Need opinion on this:
    You have a year round constant heat load, load average is 110 % split betweeen two machines 7/24. With O/A temps in the winter dropping as low as 25 but averaging 38 - 48, would you realy need the cond. fan VFD to be in place. I am looking at the cost of replacment of these items, verses doing away with them. We are seeing a replacment of at least one to two every lighting storm in the area. Lets face it, those VFDs are not the highest quality item on the market. .....
    Next pet pea of mine now that I am working these little monsters, it the EXV. COME ON TRANE >>>>> a small tip of epoxy gell to hold the little plastic cover cap over the hole at the top of the head. Was washing one the other day and that littel disk came off, WELL, do ya really need me to tell ya what happens when water gets into the top of an EXV !!! Whats the in field remady for this one ???? We are going with the high dollar fix, called a 3' pvc pipe cap with a short piece of 3' pipe to set over the EXV........
    Only problem is the PVC only comes in white !!! I'm gona paint them RED !!!
    Any takers, place your order now, supplys are limited........... Custom colors are at a higher price.......
  12. #38
    The Hot South
    That's the first time I've heard of the plastic cap coming off of the EXV head. Must have been an isolated instance.
    You need a laptop to reconfigure the unit to run without the fan inverter.
  13. #39
    Dec 2009
    Hotlanta GA.
    Well we're cookin now, high 90's in HOTLANTA now, so the air ciculation troubles are showing uo better. One solution is to run the end units and leave the middle for back up........
    I would liek to know how the smoke test was done, as in were did you set the smoke bomb, ground, top of unit, side mid way ?????
    Right now there is so much dirt form construction its just watch and see which one trips first. I don;t panic on this, ain't nothing you gona do to control mother nature !!!
    Great insight, thank you all..........