Thread: suction line sizing
-
06-16-2011, 04:28 PM #1
New Guest
- Join Date
- Jun 2011
- Posts
- 2
suction line sizing
Would someone be kind enough to answer question ...I am having a 5 ton coil R22 aprox. 57 feet from condenser to coil.. Condenser is ground level coil is 20 feet higher ... What is prefered diameter of suction line ..7/8 or
1- 1/8 ?? Is there an advantage to go next size higher or not.. Some manuals list 7/8 as minimum ...others as 1 1/8. Your thoughts Please?
Thanks
-
06-16-2011, 05:00 PM #2
Professional Member
- Join Date
- Jan 2007
- Location
- N.E. Ok.
- Posts
- 1,300
It will be determined by the mfg. and listed in the install manual.
If curious you may be able to find the manual on the mfg. web site.
-
06-16-2011, 05:06 PM #3
Regular Guest
- Join Date
- Jun 2009
- Location
- Albuquerque NM
- Posts
- 2,449
Is this a heat pump or straight AC? On heat pumps, you may need to worry about maintaining the sufficient velocity in the 20 rise section, to insure oil return to the compressor. Sometimes, they'll use a smaller size on the vertical than on the horizontal. This is a compromise to maintain the velocity while allowing the remainder of the line to be larger for a long run.
I ruled out on contractor because he wanted to use a 7/8 line on my 2.5t HP. The manufacurer allowed 3/4 or 7/8, but with the 7/8, the velocity in the vertical section would have fallen below the minimum specified by the manufacturer.
-
06-16-2011, 05:14 PM #4
Professional Member
- Join Date
- Aug 2007
- Location
- Oregon
- Posts
- 226
Traps, I would make sure you have traps put on for proper oil return
-
06-16-2011, 05:37 PM #5
Different refrigerants have different requirements based upon flow velocities, no answer possible.
Different brands and types have different requirements, no answer possible.
When the evaporator is above the condensing unit DO NOT use oil traps, they are not required and increase losses.
An inverted trap SHOULD be at the evaporator that routes it 1 or 2 inches above the top row of tubes of the evap.
As far as suction piping goes, 57 feet may SOUND like a good number, however there is a term called EFFECTIVE piping length.
As a general rule, problems can begin to exist after 50 feet and one should never reach beyond 150' of effective length.
In other words, no one here can actually answer your question because we can not see it. General answers are not going to help you much since it may or may not apply.




-
06-16-2011, 06:10 PM #6
I agree.
Traps are used to keep oil in the compressor, when a compressor is above the coil.
An inverted trap at a coil prevents all the oil/liquid in the entire system from draining down to the compressor. This prevents the compressor from having to fight against this heavy load of startup. This is used when the coil is above the condensor.
OP:
Your putting the cart before the horse. Find your manufacturer FIRST, then look at what is required, via the manufacturer.
For example. (working off of memory, don't quote my numbers, only ment to prove a point)
If I were to install a carrier 14 seer heatpump, 410a, 5 ton, 50 ft completely horizontal lineset, according to carrier's documentation I'd probably loose about 6% CAPACITY (not efficiency) with 7/8.
If I were looking at the exact same everything, but with goodman, their chart would claim 10%."Better tell the sandman to stay away, because we're gonna be workin on this one all night."
"Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."
"Just get it done son."
Dad adjusted
-
06-16-2011, 06:27 PM #7
Professional Member*
- Join Date
- Dec 2004
- Location
- newton,mass.
- Posts
- 6,109
Two things ... how's about listening to the guy that is actually looking right at the job ... don't think you trust him then get someone else (or more) to look at it.
Second thing ... some of the info posted is above wrong, I'm not going to say what's wrong as you may be a guy (home owner) doing the job (or attempting to) ... how's about just getting the job done right by someone who knows how.
."Nothing else can poison our culture, corrupt our society or ruin the character of our people like unearned money or unearned opportunity." -- James R. Cook
"Fooling around with alternating current is just a waste of time. Nobody will use it, ever." Thomas Edison, 1889.
-
06-16-2011, 10:18 PM #8
Banned
- Join Date
- Jun 2005
- Location
- Winston-Salem NC
- Posts
- 1,133
If I have a question about line sizing, I take a few measurements and call the manufacturer's tech support number, before I start buying equipment.
-
06-17-2011, 04:18 AM #9
Regular Guest
- Join Date
- Dec 2005
- Posts
- 114
The poster didn't say heat pump. He did say R-22... hmmmmm....In this day and age?
-
06-19-2011, 02:46 PM #10
Regular Guest
- Join Date
- Mar 2011
- Location
- California
- Posts
- 16
1 1/8