06-19-2011, 12:44 PM #14
Oh, I for sure ain't going to start guessing. I am guessing on what to check if you want to say that. But I ain't guessing on what to replace!
I always checked to make sure the connectors were pushed on good but didn't think to check the actual wires pushed into the plastic piece. Thanks for the idea.
-
06-21-2011, 12:29 PM #15
The easiest way to check your t-stat (klixon) is: whith the chiller running touch the motor area, right below the motor terminal plate, those motor winding t-stats open at 221°F and re-close at 180°F, if they are in fact protecting the motor on high temp you should be able to feel it (hot), with a suction SH of 4-5°F the motor should be cool, if that is the case you have a t-stat out of calibration and you need to find which of the 3 is and by-pass it.What's another word for Thesaurus?
- Steven Wright
-
06-21-2011, 07:52 PM #16
Alright guys, I checked the chiller out today. Everything was normal. I have come to the conclusion that it is one of the t-stats that is a nuisance trip. If you have been readin along you know that I have already replaced the MCSP, since it wasn't de-energizing the male unload solenoid. But I believe the damage has already been done to one of the stats being I had reset it over a couple of days until I found the problem. It's probably a weak t-stat now and opens prematurely. After coming home and reading your post Manu1, it has to be the case because I have felt the compressor a couple of times after it has tripped and it never felt hot. I didn't know that they were under the terminal plate, but I have felt the suction end where the windings are at, which was cool with a little sweat...all the way to under the terminal plate, which was cool/warm. By the way, where did you get information about the winding stats? I only found what temp they open at and that's all! Thanks everyone for the help.
-
06-21-2011, 10:16 PM #17
Professional Member*
- Join Date
- May 2000
- Location
- Houston, TX, USA
- Posts
- 216
Had a similar issue on a comp with nuissance trips. Found issue to be the terminals for the stats were sweating and causing them to rust and therefore did not have a good contact. Resolved by cleaning terminals at comp withs some sand cloth and then connecting wiring and coating with corrosion inhibitor. SP400 I believe, got if from Grainger.
-
04-20-2012, 01:21 PM #18
Regular Guest
- Join Date
- Apr 2012
- Location
- So. Fl.
- Posts
- 55
RTAA hi mot. Temp. Resolved
Bklyntek, here, hope all is well. Had a similar problem last
Year. New contract, owner had RTAA070.compB tripping hi
Motor winding temp. Stumped me for awhile, finallyclimbed
On top, found c fans right behind bad. My fault assummed
They were for ambient controlled. Well, changed both and
Never had a problem to this day. At same time, changed
Both oil filters on.compressors. Just thought I'd chime in,
Take care, guys.
-
04-21-2012, 04:08 PM #19



Reply With Quote