    Confused troubleshooting 3phase compressor please help

    i have this compressor a tecumseh AV190TT-045-S7

    460V 3PHASE 60HZ
    5 TON R22 compressor hermatic compressor

    here is my question this is a replacement compressor installed a month ago everthing was done correctly to my knolage flush high acid filter drier and vaccum what its doing is nothing!!!!

    ive checked the windings and none are open and none are grounded
    ive got the correct voltage coming to the compressor each leg and leg to leg
    ive tried to check the amp draw but its not pulling anything or even trying to come on ive never seen this before in my life

    the only thing i could think of is on the windings from when i ohm ed each leg had the same continuity i believe it was around 4.3 i am kinda rusty to the hvac industry do to taking a different job but still should be able to figure this out they shouldnt have the same continuity should they???? or is that ok on 3phase im not real sure and anything would be appriatated

    im 99% sure the compressor is bad but there is still that little bit bothering me

  2. #2
    Join Date
    Aug 2010
    Location
    honolulu, hawaii
    Posts
    124
    Ohm phase to phase, 3ph. Should all be very near the same
    Each leg at comp terminals to gnd, 0L at ALL phases.
    If contactor is in ......line side to load side power is passing and compressor still is not running.
    Compressor is bad.
    Actually check while contactor is closed line and load sides to ensure power is passing.

    Last thing to check, there's no internal overload.....see schmatic drwng.....
    What type of unit??

  3. #3
    Join Date
    Jun 2011
    Location
    NJ
    Posts
    14
    long story short, Feel the top of the compressor.. If its smoking hot its out on overload.. Leave it off overnight, start it up in the morning. If you have 460v on every combo going into the compressor, write up the compressor..

  4. #4
    Join Date
    Jun 2011
    Location
    Texas
    Posts
    13
    it is a carrier 10ton rooftop package unit when i ohmed phase to phase they were pretty close to the same and none were grounded and i had full power going to the unit with the contactors closed i just never seen one do that they usally hum or will have a winding open or somthing just figured it would alleast try with the windings good and power to the comp. thanks alot for the help just making sure im not crazy

  5. #5
    Join Date
    Jun 2011
    Location
    Texas
    Posts
    13
    yeah i know when a compressor is in overload it will have a open leg i belive common to start right?

  6. #6
    Join Date
    Jun 2011
    Location
    NJ
    Posts
    14
    God only knows whats going on there, Some compressor just break internally and seize up.. If its not out on overload replace the compressor..

  7. #7
    Join Date
    Jun 2011
    Location
    Texas
    Posts
    13
    yeah thats all i could figure thanks for the help i just never seen one do that before so i figured i would check around on the internet and see if anyone else has

  8. #8
    Join Date
    Oct 2010
    Location
    Baton Rouge, LA
    Posts
    1,112
    bubba add your email to your profile <but not on the forum page> and i will send you some info.
    If you're too "open" minded, your brains will fall out.
    Artificial intelligence is no match for natural stupidity.

  9. #9
    Join Date
    Jun 2011
    Location
    Texas
    Posts
    13
    Doin it now thanks

  10. #10
    Join Date
    Oct 2010
    Location
    Baton Rouge, LA
    Posts
    1,112
    You got mail
    If you're too "open" minded, your brains will fall out.
    Artificial intelligence is no match for natural stupidity.

  11. #11
    Join Date
    Jun 2011
    Location
    Texas
    Posts
    13
    Thanks alot man

  12. #12
    Join Date
    Sep 2010
    Location
    Florida
    Posts
    88
    Quote Originally Posted by bubba_v2008 View Post
    yeah i know when a compressor is in overload it will have a open leg i belive common to start right?
    Three phase compressors don't have common, run or start windings, each winding has the same resistance, that's why the ohm readings should all be about the same and that's why there's no run or start cap.

  13. #13
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,433

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event