Results 1 to 3 of 3
  1. #1
    Join Date
    Jul 2014
    Location
    hampton roads va
    Posts
    50

    YT optiview control issues.

    Recently I have just joined the forum. I posted earlier about a harmonic issue with same chiller. The vsd on this machine originally failed. I then replaced the vsd to find that the logic filter board also took a hit and was bad. Now 1 week later after chiller was back online. My optiview control panel keeps coming in and out. It will load up go through all the pre steps and when it goes to load the main screen it goes completely black. Im thinking the power supply module may be bad. Any help would be appreciated.

  2. #2
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,350
    replace the power wiring harness from the power supply to the microboard and your problem will probably be solved...it is an undocumented issue. also, get the 12" wiring harness...not the 8" wiring harness. yes, they make 2 lengths. no, i don't know why.
    "Mother" is the name for God on the lips and hearts of children....The Crow

  3. #3
    Join Date
    Jul 2014
    Location
    hampton roads va
    Posts
    50
    Thanks Jayguy for the help I will try that. I appreciate the help sir.