    Fryer kicking off

    I have a Pitco Frialator E/12 that heats up once then pops the high limit switch. Is it the thermostat or is it the high limit switch?

  2. #2
    Join Date
    Mar 2006
    Posts
    1,135
    Post Likes
    replace them both. its what i do, there is no reason not to do both at the same time.
    it'll take you longer to figure out which one it is, then to just replace them

  3. #3
    Join Date
    Mar 2008
    Location
    Over the river and through the woods
    Posts
    120
    Post Likes
    What Marter says....

  4. #4
    Join Date
    Jun 2011
    Posts
    2
    Post Likes
    Thread Starter
    Thanks will do!

  5. #5
    Join Date
    Jun 2011
    Location
    northern California
    Posts
    13
    Post Likes

    It's the operating stat, not the high limit.

    Measure the oil temperature. If it goes over 400ºF before popping, the high limit is doing its job. Many Bob Shaw operating stats fail open because of condensed grease gumming up its push rod. The high-limit stat is more robust.

    NEVER jumper out the high limit or you're sure to have a fire because then BOTH stats are failed and the temperature will quickly reach autoignition. Kitchen staff are tempted to jumper out to high limit to get through a rush time. Always check for a correctly wired high limit whenever you service these fryers. Sometimes they just short the "blue bird" connector under the thermopile ferrule nut, and you can't tell by just looking.

  6. #6
    Join Date
    Aug 2005
    Location
    iowa
    Posts
    1,649
    Post Likes
    or it could be the gas valve sticking open. ive had both honneywell and robertshaw valves stick open.

  7. #7
    Join Date
    Jan 2010
    Posts
    13,240
    Post Likes
    Well now you might as well go buy a new deep fryer

  8. #8
    Join Date
    Oct 2010
    Posts
    67
    Post Likes

    Talking

    Quote Originally Posted by bernardc View Post
    Measure the oil temperature. If it goes over 400ºF before popping, the high limit is doing its job. Many Bob Shaw operating stats fail open because of condensed grease gumming up its push rod. The high-limit stat is more robust.

    X2, But if you want replace the thermostat, high limit, and gas valve

  9. #9
    Join Date
    Oct 2002
    Location
    Lady Lake, Florida
    Posts
    799
    Post Likes
    That made sense to me that the thermostat could fail open. I've only worked on a couple of fryers in the past. Don't most do a warm up when starting, to cycle the heat to gradually heat up the oil or is that only on certain types of fryers?

  10. #10
    Join Date
    Jul 2011
    Location
    Elk River, MN
    Posts
    1
    Post Likes

    Thumbs up

    Quote Originally Posted by marter View Post
    replace them both. its what i do, there is no reason not to do both at the same time.
    it'll take you longer to figure out which one it is, then to just replace them
    X2

  11. #11
    Join Date
    Jan 2005
    Location
    Red Deer,Alberta
    Posts
    54
    Post Likes
    By the date I see probably resolved one way or another but I was going to say that sometimes the high limit capillary tube can touch against the element and of course would overheat.Does this model have the element interlock switch that opens to keep fr.energising when elements are up?If does maybe check for phantom issues.

  12. #12
    Join Date
    Jun 2006
    Posts
    308
    Post Likes
    just bypass in see wheb unit turned on while checking temp.

  13. #13
    Join Date
    Nov 2000
    Location
    Memphis TN USA
    Posts
    6,969
    Post Likes

    test before replacing

    Anybody that says change without testing is not right.

    Your job is to inform the costumer, then follow their instructions
    1st find out what is not doing its job.
    2nd jump out a part if possible to test another part
    3rd tell the costumer how much it cost to fix the problem
    4th advise the costumer about potential problem that might cause the repair to get more expensive (if possible)

    If the limit cuts out at 400F it is doing its job.
    If the fryer is getting above 400F, is the thermostat closed. It could be a gas valve.
    If the limit cuts out below 400F, jump it while you test the t'stat.
    When you have a good understanding of the problem, talk to the costumer.
    Stop studying the fryer when the cost to repair start getting close to the cost to replace. A new fryer cost $750. A gas valve costs nearly that much.

    Problem comes in when it acts normal during your test. Hard to diagnose intermittant problems.
    If the superheat ain't right it ain't charged right.