    Einstein controller oil sep alarm

    worked on a small rack system today with a einstein controller,
    had a oil SEP alarm, checked oil separator gauge on filter was good, all compressors oil safetys were not tripped, and sight glasses were good, normal status and all circuit temps were fine and not alarming.

    just wondering what would may of cause this controller to alarm even though things appear to be normal.
    I'm just learning on this controller. Ive seen controllers before monitoring and send out alarms and things are okay.

  2. #2
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,547

  3. #3
    Join Date
    Jul 2005
    Location
    Southern California
    Posts
    585
    Is this a Temprite separator and the guage you said looked good is is the pressure differential indicator?

  4. #4
    Join Date
    Nov 2010
    Location
    Southern Maine
    Posts
    10
    It was a temprite separator and the pressure differential indication was between the green.
    wasn't even close to yellow or red.

  5. #5
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,547
    Quote Originally Posted by hvactech88 View Post
    It was a temprite separator and the pressure differential indication was between the green.
    wasn't even close to yellow or red.
    Did you measure any pressures?

  6. #6
    Join Date
    Nov 2010
    Location
    Southern Maine
    Posts
    10
    no i didn't i should of checked, im on call for the weekend but if that comes in again i need to look into it more..

  7. #7
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,547

  8. #8
    Join Date
    Dec 2010
    Location
    new jersey
    Posts
    366
    I'm curious about this....can someone explain,I have not seen this type myself.

    I'm guessing from reading the post, the gauge will sense a diff. in press. and will indicate this on the dial by indicating yellow or red depending upon the diff. in press. indicating a clogged element.

    and then this is also connected to a digital input in the Einstein controller?

    I commonly see Henry separators and turbashed. but not this ,yet, anyway.

  9. #9
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,547
    A temprite separator has a paper element inside. Like any filter element, the filter loading is measured by pressure drop.

    A pressure drop of around 10# is threatening to burst.

    I've found 2 burst elements this year.

    They make a little diff pressure switch the does hook to a controller for alarming. That is why I asked the first question.

  10. #10
    Join Date
    Aug 2002
    Location
    Orange County CA
    Posts
    1,084
    I have seen them with a D.I. to an input...I think that's fancy and neato.

    I second the sep service.

  11. #11
    Join Date
    Jun 2011
    Location
    Barbados
    Posts
    34
    Quote Originally Posted by jpsmith1cm View Post
    A temprite separator has a paper element inside. Like any filter element, the filter loading is measured by pressure drop.

    A pressure drop of around 10# is threatening to burst.

    I've found 2 burst elements this year.

    They make a little diff pressure switch the does hook to a controller for alarming. That is why I asked the first question.
    Thanks for the explination. I work on quite a few racks and I've not seen this type before, i think its a cool feature though.

  12. #12
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,547
    Quote Originally Posted by Gnarly View Post
    Thanks for the explination. I work on quite a few racks and I've not seen this type before, i think its a cool feature though.
    The pressure switch is an option. I've only seen them in catalogs...

    I just put a little chart up where I can record the pressure across the filter.

  13. #13
    Join Date
    Dec 2006
    Location
    In a Mess
    Posts
    1,008
    Ive set a notice and alarm for a pres diff across filter and it seemed to work Good!
    if in doubt replace!! haha
    Sig removed by mod. G-Rated site

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event