    York PRTU's

    Is anybody having problems with York unit's economizers not working properly? We have quite a few York units that - on a 97 degree day with humidity you could nearly swim in - we are finding that on no a/c calls the economizers are wide open with both compressors running for all their worth. They utilize the Simplicity boards, which I am beginning to wonder if they have issues York isn't letting on about.

  2. #2
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    17,884
    Quote Originally Posted by geecee View Post
    Is anybody having problems with York unit's economizers not working properly? We have quite a few York units that - on a 97 degree day with humidity you could nearly swim in - we are finding that on no a/c calls the economizers are wide open with both compressors running for all their worth. They utilize the Simplicity boards, which I am beginning to wonder if they have issues York isn't letting on about.
    Does the econ respond when you open or short the enthalpy sensor leads?

    I haven't found the condition your describe. You are talking about the Coleman Line Yorks, correct, where the control bay door opens to the left against the econ hood?
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  3. #3
    Join Date
    Apr 2007
    Location
    Pa
    Posts
    758
    I had two 5 or 6 ton units do that last summer

  4. #4
    Join Date
    Jun 2006
    Location
    New Jersey
    Posts
    4,330
    Quote Originally Posted by geecee View Post
    They utilize the Simplicity boards, which I am beginning to wonder if they have issues York isn't letting on about.
    So when you checked the economizer modules.....you found what? How did you fix them(hopefully not by just disconnecting the econo)? Was it because the remote pot wasn't jumped? More detail?

  5. #5
    Join Date
    Apr 2007
    Location
    Pa
    Posts
    758
    In my situation, the economizer would stay open 100% on a 95 degree day. Talk to york and they said" it was an internal control issue on the economizer control"