    This evaporator coil appears to be several years older than dirt.
    McQuay
    M. # RLC-200B F
    S. # 3302058
    Four 1/20 HP fans on it.
    Is it as easy as it being a 20,000 BTU coil ? <g>
    If not; what is the secret code which reveals it?
    PHM
    Jul 2000
    Cuenca, Azuay, EC
    Yes, it's that easy.
    The capacity is 20,000 Btuh at a 10F TD.
    If you need parts, go to Heatcraft. The McQuay line was bought up by Snyder General, the RLC design was then under the Chandler brand which is now part of Heatcraft.
    Thanks Ice -
    It's for a country club's beer box. They installed it all used maybe 15-20 years ago and it looked like something I would have been a little apologetic about giving to the scrap guys even back then.
    With 8 subcooling and the R-12 valve wide open it is running about a 5 lb. suction pressure and an 80 SSH. Think I'll try a new valve and see what happens.
    Also; cannot get the screws out of the motor mounts - so that will need to be cut off I guess. I wonder if anything like a motor mount is still available? <g>
    PHM
    Quote Originally Posted by icemeister View Post
    PHM
    Jul 2000
    Cuenca, Azuay, EC
    Here's a link to the Heatcraft Interlink parts listings for Chandler:
    http://www.heatcraftrpd.com/products...s/CH-CC-IN.pdf
    It looks like you may have an "F" vintage, but call them and with your Mod/Serial numbers, they should be able to tell you if the mounts are still available.