    Quote Originally Posted by CoolWine View Post
    Nice looking install.

    Why the insulated LL?
    On ductless split systems the "liquid line" is acutally a mixed phase line and part of your evaporator because your metering device is at your condenser so you are required to insulate it so you don't boil off to much refrigerant before it hits your evaporator coil.

    Correct me if I am wrong on this particular system.

  2. #15
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    34,316
    Actually in this case, Eric said their was a TXV in the wall unit so the insulated LL wasn't needed. But it called for 1/4 x 3/8" lineset, easiest to get was a mini split lineset kit.

  3. #16
    Join Date
    Nov 2007
    Location
    Texas
    Posts
    223
    how big is the room and cond. unit?