    Frown RTAA140 Trane unit running crazy!!!

    I have a RTAA air cooled trane chiller that has 2 circuts on it. I have had problems with circut #1 going in to a alarm that is 1B7 that is a compressor overload alarm then it will have a code for low oil flow, then it will have a alarm on the condenser pressure being high and then a loss of comunication, then a alram on the evap. pressure being low. I fixed to leaks on this circut, Turned the power back on. Let oil warm for 45-60 MIN. turn the switch back to atuomatic mode, then before the compresser even started, it was locked out on compresser overload again!!! Starting to wonder if the microprosser board might be going bad. My coil is clean all condenser fans are coming on when it runs. THis makes the other circut run @ a overloaded state to up to 120% then it will shut down..
    Has anybody seen these symptoms ?? Is the board flaking out ??? I checked all the conections with the little plastic tool trane gives you and reconcted all the plugs and jacks as well. THere is 5 microprosser boards on this unit and they all have to "talk" to each other.
    And lets not talk about the "ice Mode" !!!

  2. #2
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    Quote Originally Posted by fool4school View Post
    ...And lets not talk about the "ice Mode" !!!
    are you running this unit in ice making mode?

    and yes, all of the boards need to talk to each other.
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  3. #3
    Join Date
    Feb 2011
    Location
    Indianapolis, IN
    Posts
    34
    Post Likes
    Thread Starter

    Frown

    Yes, it dose have a ICE mode. When both circuts are working it will make about 60-70% of ice. I have it running 9 hours in ice mode. But, if one circut shuts done you can forget about making any ice to any kind of level it burns off fast in the daytime.. Im sure this was a good system 12-15 years ago but it has become very cumbersome and very erratic in its old age.

  4. #4
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    4,011
    Post Likes
    Im sure this was a good system 12-15 years ago but it has become very cumbersome and very erratic in its old age.[/QUOTE]


    This is what happens to poorly maintained/serviced equipment . Particularly when the work is performed by techs who are not knowledgeable about this particular piece of equipment .
    The RTAA is the small and larger tonnage version is a great chiller . I look after several of them and some of them are 98 vintage . Still humming along quite happily . Have they had problems ....of course there mechanical pieces of equipment . I wouldnt have a job if stuff didnt need service .
    Good proper service by knowledgeable techs goes a long way to equipment reliability and longevity .
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech, I’m retired ….I used to be a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  5. #5
    Join Date
    Jul 2005
    Location
    Melbourne Fl
    Posts
    39
    Post Likes
    Do you have IOM manual?

  6. #6
    Join Date
    Jan 2009
    Location
    Tampa
    Posts
    1,467
    Post Likes
    Quote Originally Posted by fool4school View Post
    I have a RTAA air cooled trane chiller that has 2 circuts on it. I have had problems with circut #1 going in to a alarm that is 1B7 that is a compressor overload alarm then it will have a code for low oil flow, then it will have a alarm on the condenser pressure being high and then a loss of comunication, then a alram on the evap. pressure being low. I fixed to leaks on this circut, Turned the power back on. Let oil warm for 45-60 MIN. turn the switch back to atuomatic mode, then before the compresser even started, it was locked out on compresser overload again!!! Starting to wonder if the microprosser board might be going bad. My coil is clean all condenser fans are coming on when it runs. THis makes the other circut run @ a overloaded state to up to 120% then it will shut down..
    Has anybody seen these symptoms ?? Is the board flaking out ??? I checked all the conections with the little plastic tool trane gives you and reconcted all the plugs and jacks as well. THere is 5 microprosser boards on this unit and they all have to "talk" to each other.
    And lets not talk about the "ice Mode" !!!
    i am not a pro!
    i would start with the ipc wiring,(connections) also , the differantial pressure , if not correct , will cause problems, then check ur oil circuit, then u say condenser pressure, why is the machine not rejecting the heat, ? did u perform test on txv?
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

  7. #7
    Join Date
    Jan 2009
    Location
    Tampa
    Posts
    1,467
    Post Likes
    high condenser pressure will cause loss of oil flow alarm., due to the higher pressure the oil moves faster and throws this alarm,
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

  8. #8
    Join Date
    Dec 2009
    Location
    Fort Worth, Texas
    Posts
    154
    Post Likes
    oil flow is caused by oil filter, worn rings on check valve, high condensing pressure also if your saturated condenser or oil thermistors are not reading correctly.
    temp drop across oil cooler should be around 20 degrees and oil drop across filter, check and solenoid should be around 10 psi
    but the first thing you going to have to do is clean condenser coils or replace fans to get head down.

    good luck

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •