Insulating Ducts with Bubble Foil AND Fiberglass Insulation?
Hi- I just finished cleaning and sealing all return and supply ducts with mastic and insulating the attic floor to R-30. Now I'm about to start the duct insulation and the sealing electrical/drywall gaps etc.
I have a couple concerns about the duct insulating and future condensation.
I live in Fort Worth, TX so it gets hot and can be humid. I have this crazy idea of using bubble wrap insulation (I'm not here to debate it's worthiness at all) and then using fiberglass with aluminum backing on top of the bubble wrap.
My thinking behind this has nothing to do with the insulating qualities of of the bubble wrap since I don't plan to do all the labor required to get the air gap between the duct and the foil. I'm thinking about the bubble wrap for it's vapor barrier and air sealing potential, the r-1* that it would provide between the duct and fiberglass is just a bonus in my reasoning.
If I wrap the ducts with the foil bubble wrap insulation (marketed as radiant barrier) directly on the ducts while sealing it with aluminum tape and then wrap over that the aluminum backed fiber glass insulation, aside from this possibly just being unnecessary and obsessive, is there any detrimental affects that could occur from condensation (rust/mold) within the layers if applied as mentioned?
I can clarify and post additional information, if needed. In my head this sounds like a decent idea, but I just don't know if it's a complete waste or even worst, if I could create a mold or rust problem in the future or ruin the r-value of the fiberglass from this configuration.
I've got a couple more days of brainstorming before the actual work gets done so all possibilities are welcome.
Thanks in advance.
Eli.
-
06-07-2011, 06:52 AM #2
Professional Member*
- Join Date
- Jun 2010
- Location
- Philadelphia PA
- Posts
- 2,139
ou may have this backwards
With the vapor barrier in mind, I think the FG wrap first then the bubble wrap as a second vapor barrier,in contact with the Wrap Vapor barrier is better.
Please understand that it is very difficult to maintain the integrity of the Wrap Vapor Barrier so how is it that the duct doesn't sweat unless there is a large tear in barrier? It is because a small/ expected amount of leakage will put relatively dry air in the insulated space between duct and vapor barrier.You have got to learn from other people's mistakes! Because God knows you don't live long enough to make them all yourself !!!!!!!!
-
06-07-2011, 11:46 PM #3
New Guest
- Join Date
- Jun 2011
- Posts
- 3
maybe... but
Well... I was thinking I could have it backwards too, but here is my reasoning for putting the bubble foil FIRST:
1) People typically use the bubble foil by itself and I'm guessing that in many installations they fail to get the air space between the bubble foil and the duct OR overtime that airspace collapses for various reasons and there is direct contact of one of the foil's vapor barriers with the duct. The manufacturers of the bubble foil even recommend using the bubble foil as the material for the spacers to get the air gap in many cases... so, if condensation that would cause rust would be common from this, I probably would've heard about it or read about it in another thread somewhere?
2) If I put the fiberglass first, I'm running the risk of future owners ripping everything out and doing tons of unnecessary work because they see the bubble foil on top and automatically think "snake oil" and "garbage" ... or I'm running the risk of an inspector failing the job because they don't understand what's actually happening ... or even worst, I'm running the risk of one of the future HVAC contractors coming in and selling the future owner on a reinsulation job that is actually much more expensive and inferior to what I can do right now if I can just get my science straight before beginning the work.
The attic gets really hot right now (I have plans for a radiant barrier, but need to get the ducts finished first). I've been taking daily temperature readings at 140F around 3pm and the air pushing through the ducts will be coooooold once I get the unit all attached and powered up. The fiberglass insulation that was on the ducts already had plenty of small pin holes and the previous owner/installer didn't wrap any insulation under the plenum due to awkward positioning which creates extremely demanding physical labor. So... it is somewhat comforting that you say there is an expectation of the fiber glass's vapor barrier being imperfect... with this in mind, if the bubble foil outer layer were to receive condensation at the fiberglass contact, it probably would dry out quick enough or be as if it were in direct contact with the duct metal making it no more of a condensation hazard than it would be without the bubble foil in place?
Just thoughts.
I was also thinking that if the bubble foil goes on as the outer wrap the moisture problems could be worst because the bubble foil acts as a near perfect vapor barrier... so any moisture that gets in there won't find a way out too easily when it can just sog up the fiberglass or if it can sit between the fiberglass foil and the bubble foil.
-
06-08-2011, 02:44 AM #4
Regular Guest
- Join Date
- Nov 2010
- Posts
- 149
In cases like these it would be hard to find someone who tried this before and who knows based on experience, so you'd have to rely on physics. Warm air holds more moisture than cool air, and condensation occurs on duct surfaces when a large volume of air is cooled enough by the duct surface. Faced insulation helps because there's only a little bit of air hugging close to the surface of the duct that can cool enough for condensation, plus the facing prevents more humid air from coming into the insulated space. Let's say you put foil first. The outside of the foil would be warmer than the inside, so the air trapped inside the fiberglass layer would not get as cool as if it was directly against the duct without the inner foil layer. Therefore condensation is even less likely. Based on physics I doubt you would have condensation problems, in fact I think your idea would help because you have a double vapor layer preventing new humid air from getting close to the cold duct.
-
06-08-2011, 08:30 AM #5
You expressed a concern about future owners thinking your ducts are bad because they look different. If you could get a duct leakage test from a professional, and also a static pressure test, that would document how good your system is. And likely would reassure future owners. I have reasonably high confidence you will apply lots of mastic and the result will be good sealing. This is the kind of thing I expect a homeowner will do well because he really cares about the result more than the time spent. No disrespect meant to HVAC professionals, but this is a job with a high labor/payment ratio is it not?
I sure wish we could invent cheap wireless moisture sensors and apply them to see when the dreaded condensation actually happens. We could learn more by comparing actual results to theoretical, where it most matters.
Best of luck -- Pstu
-
06-08-2011, 01:58 PM #6
Professional Member*
- Join Date
- May 2004
- Location
- south louisiana
- Posts
- 2,179
I've seen ductwork with double vapor barriers
the insulation condensates between the vapor barriers
and the insulation value is zero.
I wouldn't ever do it. even on hard pipe the ductwrap should
be single layer..lots of folks insulate over existing ductwrap
as an 'upgrade' this actually causes more problems as the
hard pipe has lots of leakage sites and this moisture is drawn
into the duct system.
not a good idea...and in my hot humid climate...a really really
bad idea.
imo it is a lot of labor for no benefit.
your mastic sealing will provide the air seal.
best of luckThe cure of the part should not be attempted without the cure of the whole. ~Plato
-
06-08-2011, 02:15 PM #7
Regular Guest
- Join Date
- Nov 2010
- Posts
- 149
I believe what you observed is true, but I have a hard time believing this based on physics unless there were some leaks in the ducting (in which case it's a problem with leaky ducting, not because of double layers of insulation). Can someone explain this based on physics to place the blame on the double insulation? The laws of physics don't change, so I tend to think this result occurs because people who "upgrade" by adding another layer are failing to check the metal duct work for leaks.
-
06-08-2011, 07:21 PM #8
Professional Member*
- Join Date
- Jun 2010
- Location
- Philadelphia PA
- Posts
- 2,139
I like Energy rater's explanation
She is not talking about double insulation, but rather double vapor barrier with duct wrap and like the general Building Science rule about double vapor barriers capturing moisture, double wrap does just that.
I do think since ther is no Fuzz in the bubble then the either way the duct/bubble or wrap FSK/bubble would be a double barrier and no sandwich like the double wrap problem
Hows that explanation sound to Energy and Scorpion?You have got to learn from other people's mistakes! Because God knows you don't live long enough to make them all yourself !!!!!!!!
-
06-08-2011, 07:45 PM #9
Thoroughly sealing the ducts is the first priority. Using a good non-hardening mastic is best and using a backing where there are large holes is better. Once the duct is thoroughly sealed, you can use a duct blaster to check it for additional, undiscovered leaks. Get it as tight as possible, then insulate.
The concept of moisture barrier and thermal efficiency are two entirely different issues. The moisture you should be worried about isn't what's in the ducts, it's what's in the attic! If your ducts are tight, there is only thermal transfer about which to be concerned.
Think of it this way. The duct is tight, so nothing is leaking out or in. It's just a conduit through which the room air will travel.
The insulation is another issue entirely. So let's have a look at the dynamics. Let's assume the duct temperature is 55°F and the attic is 140°F. Let's also assume that the dew point of the air in the attic is 90°F. We can now see, that if 140°F attic air can come in contact with anything that is 90°F or lower in temperature, condensate moisture will appear. So the trick is to keep the air of 90°F or less, totally away from the attic air. Now we just need to understand that the conduction of warm temperature migrates inward toward the duct (heat always flows from warmer to cooler, right?) at some point, the 140°F temperature is going to cool down to 90°. Where, at what depth of the insulation that temperature is reached is a function of the R-factor of the insulation. But, if the exterior of the insulation is moisture tight, then there is no moisture to condense out of the temperature in the insulation when it reaches 90°F or less.
So as you should be able to see, it's keeping the insulation moisture barrier sealed so the hot, damp air can't penetrate. Then we don't care about dew point within the insulation as the outer surface will always be above 90°F and therefore no surface condensate will appear. If you allow the moisture barrier of the insulation to be penetrated, then you'll indeed end up with wet insulation. And if you use insulation that's too thin (low R-factor) then the surface of the insulation may be 90° or less and condensation will form on the surface.
So seal the ducts, use a very high insulation R-factor with a good, sealed moisture barrier on its exterior and you won't have any condensation issues. Try and defeat the laws of thermodynamics and, well, just don't do that and you'll be okay.
-
06-08-2011, 08:08 PM #10
Would your explanation work with 75-80 dew point? I think it would. Because 90 is pretty extreme, like in Arab Gulf island regions. I don't think anywhere in the USA is likely to exceed 80.
I have a ventilated attic and we see 75 dew point during the summer. Measurements in the attic are well under that -- not explaining why just what is observed.
Thanks -- Pstu
-
06-09-2011, 10:39 AM #11
Professional Member*
- Join Date
- May 2004
- Location
- south louisiana
- Posts
- 2,179
ok so I thought a lot about this last night when I couldn't sleep.
I try to stay away from all the mathimatical calculations, as most of
my clients want answers, not calculations or theories. they don't hire
me to confuse but to solve. sometimes y'all make my head ache with all the
calculations..I'm just sayin..LOL

Reply With Quote