  1. #1
    Join Date
    Jul 2005
    Posts
    6

    Hmm

    I think i have read that superheat should run around 30*.
    I check the charge on my new unit last night and the direction for charging by superheat. Hears my question
    Why is it that newer units superheat runs lower then then the 30* that I think I have read?
    thanks txg.

    As for my unit the OAT=76*,RA=70*,SP=73psi,st=56*,and last sat.suction temp=42* which gives me a 12* superheat, chart called for 10* superheat.

  2. #2
    Join Date
    Feb 2005
    Posts
    344

    Superheat

    You may have read wrong? :-)

  3. #3
    Join Date
    Oct 2004
    Posts
    3,400
    Long list.

    Here's a few...

    Wrong charge, coil, ductwork, filter, air handler, metering device, equipment, to name a few.

    Could be any one of the above, more than one of the above, or none of the above.

    Happy hunting.


    [Edited by bwal2 on 09-09-2005 at 10:13 AM]

  4. #4
    Join Date
    Sep 2001
    Location
    Vancouver Canada
    Posts
    996
    superheat requirments will change with load on the unit, where did you read that you needed 30 degrees superheat? Seems a bit high to me. Also from the looks of your calculations you are actually running 14 dgs sheat and not 12.
    "Go big or Go Home"

  5. #5
    Join Date
    Jul 2003
    Location
    Massachusetts
    Posts
    288
    Originally posted by Black Adder
    Also from the looks of your calculations you are actually running 14 dgs sheat and not 12.
    which may be good for your system depending on all the factors stated above.
    "ok, everyone just calm down."

  6. #6
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    68,923
    Not sure what you are calling superheat. The only time Goodman chart states 30Ί superheat is if the return air temperature is 75Ί and the ambient temperature is 60Ί, which is not a very good time to be checking system charge.

    I think you may have some terminology misapplied.
    Government is a disease...
    ...masquerading as its own cure…
    Ecclesiastes 10:2 NIV


Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event