Thread: Goodman superheat Q

  1. #1
    Join Date
    Jul 2005
    Posts
    6
    Post Likes

    Hmm

    I think i have read that superheat should run around 30*.
    I check the charge on my new unit last night and the direction for charging by superheat. Hears my question
    Why is it that newer units superheat runs lower then then the 30* that I think I have read?
    thanks txg.

    As for my unit the OAT=76*,RA=70*,SP=73psi,st=56*,and last sat.suction temp=42* which gives me a 12* superheat, chart called for 10* superheat.

  2. #2
    Join Date
    Feb 2005
    Posts
    344
    Post Likes

    Superheat

    You may have read wrong? :-)

  3. #3
    Join Date
    Oct 2004
    Location
    Tyler, TX
    Posts
    3,400
    Post Likes
    Long list.

    Here's a few...

    Wrong charge, coil, ductwork, filter, air handler, metering device, equipment, to name a few.

    Could be any one of the above, more than one of the above, or none of the above.

    Happy hunting.


    [Edited by bwal2 on 09-09-2005 at 10:13 AM]
    RSES Certificate Member Specialist

    Southwest Regional Association of RSES Secretary, 2017

  4. #4
    Join Date
    Sep 2001
    Location
    Vancouver Canada
    Posts
    996
    Post Likes
    superheat requirments will change with load on the unit, where did you read that you needed 30 degrees superheat? Seems a bit high to me. Also from the looks of your calculations you are actually running 14 dgs sheat and not 12.
    "Go big or Go Home"

  5. #5
    Join Date
    Jul 2003
    Location
    Massachusetts
    Posts
    291
    Post Likes
    Originally posted by Black Adder
    Also from the looks of your calculations you are actually running 14 dgs sheat and not 12.
    which may be good for your system depending on all the factors stated above.
    "ok, everyone just calm down."

  6. #6
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    Not sure what you are calling superheat. The only time Goodman chart states 30º superheat is if the return air temperature is 75º and the ambient temperature is 60º, which is not a very good time to be checking system charge.

    I think you may have some terminology misapplied.
    Training is important!
    Practical Training is a must!

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •