  1. #1

    Kooltronics

    I have a 1 1/2 ton kooltronics cabinet AC side mount on a VFD cabinet.
    The unit has an 30/100 EPR valve (working), accumilator, has good air flow and pressures of 250 discharge, 50 suction, outdoor ambient is in the low
    70's.
    After starting the unit the suction line begins to freeze between the accumilator and compressor, shortly after the compressor shell begins to freeze which eventually freezes all the way to the evaporator.
    Im thinking I need to replace the cap tubes which are 2 x .067 x 40" and replacing the line drier as well, thoughts anyone?

  2. #2
    Join Date
    Jul 2007
    Location
    Mount Airy, MD
    Posts
    7,100
    Quote Originally Posted by jbnace View Post
    I have a 1 1/2 ton kooltronics cabinet AC side mount on a VFD cabinet.
    The unit has an 30/100 EPR valve (working), accumilator, has good air flow and pressures of 250 discharge, 50 suction, outdoor ambient is in the low
    70's.
    After starting the unit the suction line begins to freeze between the accumilator and compressor, shortly after the compressor shell begins to freeze which eventually freezes all the way to the evaporator.
    Im thinking I need to replace the cap tubes which are 2 x .067 x 40" and replacing the line drier as well, thoughts anyone?
    Without knowing SH, SC and DSH..... I would say that's a good plan

    BTW, welcome to the site !!!

  3. #3
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    14,474
    I second that.

    Get busy on your Pro membership app.

  4. #4
    Join Date
    Jun 2009
    Location
    ontario cali
    Posts
    8
    would look into the aculmator too it might be clogged had this happen before did the same thing.