    Need advice on line set and oil strap

    Hi please give me some advice and recommend ,used 3T with 7/8 SL 3/8 LL but my split SYS between condenser and coil about 15feet and 1 FT different heigh ,do I need install oil strap and can I use 7/8SL instead 3/4 SL is there any different of efficiency ,performance affect or not any suggest very appreciate .

  2. #2
    Join Date
    Jun 2011
    Location
    long island, NY
    Posts
    4
    You don't need oil trap and for residential systems you can go as high as 1 1/8 in SL its a little more efficiant. If your lines are 100 ft or more you will need a LL solinoid.

  3. #3
    Join Date
    May 2011
    Posts
    33
    HI ac andy thank for the advice but let say with 15fts can I use 7/8 " or can i uesd 3/4 " for SL which one most affective

  4. #4
    Join Date
    Jun 2011
    Location
    long island, NY
    Posts
    4
    7/8 is better. You can go larger in SL on unit specs but never go smaller. It is more efficiant but not by a lot.

  5. #5
    Join Date
    May 2011
    Posts
    33
    So let go little bit detail 3T unit , the the length SL from Condenser to Evaporator coil is 15 FTS if I do have install 7/8" line SL which is better compare with 3/4" SL or I must go with 3/4 " what would be see any different and if I go with 7/8" would see any different or any affect >?.Thank a lot

  6. #6
    Join Date
    Jun 2011
    Location
    long island, NY
    Posts
    4
    It is better to install 7/8 in case you go with a high efficiancy unit with 410a some units 16 seer and above require 7/8 - 1 1/8

  7. #7
    Join Date
    Mar 2006
    Location
    Denver/Boulder
    Posts
    2,392
    Hmmm...

    has no one read the site rules?
    What lies behind us and what lies before us are small matters compared to what lies within us.


    Two pressures, four temperatures = SUCCESS!


    Boulder Heating Contractor


    For Consumers:

    For HVACR Professionals:


Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event