Any ERV experts here
Trying to learn about the install I have coming up. RNC, house on slab, I am assuming the intake from outside will have to be a roof vent and the same for the exhaust.
Ive read that some hook into the duct system and others just dump into living space ?
Anybody ?
-
06-03-2011, 08:20 AM #2
Regular Guest
- Join Date
- May 2011
- Location
- Southern Indiana
- Posts
- 97
If you want to distribute to the entire house, hooking to the duct is best. Just have to make sure to have control to the indoor blower.
-
06-03-2011, 12:20 PM #3
Professional Member*
- Join Date
- Nov 2001
- Location
- East Texas
- Posts
- 832
-
06-03-2011, 12:33 PM #4
Regular Guest
- Join Date
- May 2011
- Location
- Southern Indiana
- Posts
- 97
Yes, it has a crossover filter and most ERV's have 6" hookup. There have been instances when I just installed 2- 6" B-Vents out the roof to hook to.
-
06-03-2011, 01:21 PM #5
Professional Member*
- Join Date
- Jan 2002
- Location
- East Grand Forks, MN
- Posts
- 1,361
ERV
I try to stay away from penetrating roofs whenever possible. Is it possible for you?
Are you using this for fresh air only or an exhaust system? With FA only, all you need is to pipe it in the Return Air, with an exhaust system you would need to vent from pick up points like bathrooms, kitchen and laundry locations etc...
You can duct it into the heating/cooling system duct with either type.
-
06-03-2011, 01:56 PM #6
Regular Guest
- Join Date
- May 2011
- Location
- Southern Indiana
- Posts
- 97
The whole idea of using a ERV system is to recieve fresh air exchange without losing too much heating or cooling. (Energy Recovery Ventilator) It is designed to pull undesirable air from a space (return) and mix and filter fresh air (outside). The air coming in through the mixer can then be fed into your supply duct and the bad air exhausted outside.
-
06-03-2011, 10:53 PM #7
Professional Member*
- Join Date
- Nov 2001
- Location
- East Texas
- Posts
- 832
I plan on keeping it seperate from the supply or return. I read some research where they tested 8 houses in Raleigh, and they determined this was the best way to install
Honeywell ERV should be here next week.
-
06-05-2011, 08:34 PM #8
Professional Member
- Join Date
- Jun 2011
- Location
- Western MA
- Posts
- 58
I typically exhaust the bathrooms and duct the fresh air to the return side of the duct system. If you duct fresh air directly into the living space you can sometime get cool draft complaints. If bathroom fans are in or ducting the bathrooms isn't easy now, you can also install a central return for the stale air exhaust. We usually vent the intake and exhaust out the side wall and not the roof.
-
06-06-2011, 08:42 AM #9
Professional Member*
- Join Date
- Nov 2001
- Location
- East Texas
- Posts
- 832
Joseph, I am doing a 12 x 12 central return to exaust the stale air. And I will tie in the incoming fresh air to the return.
I am planning on just doing the fan interlock for control. This would just involve two wires from the furnace to the ERV ( green and common ) correct ?
-
06-06-2011, 09:01 AM #10
Professional Member
- Join Date
- Jun 2011
- Location
- Western MA
- Posts
- 58
Are you doing the central air system also? If so, you can install a honeywell thermostat with ventilation controls built in. It makes for a nicer installation and honeywell has some great control options.
-
06-06-2011, 09:31 AM #11
Professional Member*
- Join Date
- Jan 2002
- Location
- East Grand Forks, MN
- Posts
- 1,361
I usually involve three wires. Some ERV come with the terminals ready and some do not and you will be required to figured it out yourself. But you don't want to power the "G" terminal other then the stat otherwise AC unit will turn on!
Like Joseph said, there are stats that have built in ventilation terminals, but cost more.
-
06-06-2011, 10:22 AM #12
Professional Member*
- Join Date
- Nov 2001
- Location
- East Texas
- Posts
- 832
Yes, this is the rough in for new resi. construction that I am doing. I would think it would be best to have the erv run only when the cetral air is running that way the incoming outdoor air will get conditioned thru the indoor air handler and coil or furnace depending on the season.
ERV model : honeywell ER150C2004
What does a honeywell iaq do diff. than a fan interlock ?
-
06-06-2011, 10:29 AM #13
Professional Member*
- Join Date
- Nov 2001
- Location
- East Texas
- Posts
- 832
[QUOTE=arc8;10378172]I usually involve three wires. Some ERV come with the terminals ready and some do not and you will be required to figured it out yourself. But you don't want to power the "G" terminal other then the stat otherwise AC unit will turn on!
Like Joseph said, there are stats that have built in ventilation terminals, but cost more.[/QUOTE
honeywell ER150, installation manual, Figure 15, shows a fan interlock diagram tied into G on furnace and G on the stat. Wouldn't that work ok in heat and cool?