Carrier problems too coincidental?
I'm missing something. two rental apartments have carrier condensing units. model #'s 38CKB036320 and 38TG030300. neither the fan or compressor is working. has power. Relay closes with 24 volts. Cap OK. I'm simply stumped. any advise would be greatly appreciated. Thank you....
-
06-02-2011, 09:59 PM #2
Professional Member*
- Join Date
- Dec 2002
- Location
- SouthEast NC ICW & Piedmont Foothills
- Posts
- 7,257
just where are you measuring the 24v?
It`s better to be silent and thought the fool; than speak and remove all doubt. 
-
06-02-2011, 10:06 PM #3
Check the hi-v fuses.
-
06-02-2011, 10:21 PM #4
Regular Guest
- Join Date
- Mar 2011
- Posts
- 18
24 volts from air handler (furnace) to condensing unit. The relay closes. As I said, power is good. I've never had a bad fan and compressor on the same unit but now I get two at about the same time and same symptoms and they are both carriers from roughly the same time period. seems too unlikely. What am I missing? I'm sure it's something silly but I can't get it...
Last edited by Zimprops; 06-02-2011 at 10:28 PM. Reason: Miss understood hi-v reply at firwt
-
06-02-2011, 10:24 PM #5
-
06-02-2011, 10:33 PM #6
-
06-02-2011, 10:35 PM #7
Regular Guest
- Join Date
- Mar 2011
- Posts
- 18
Look dunk man, I replace one with a concord dry unit this morning and probably wil do the other but there has to be something simple here. If you don't want to share fine, but maybe someone else is willing to share their knowledge...
-
06-02-2011, 10:38 PM #8
Well you said the power is good, but I don't buy that.
-
06-02-2011, 10:43 PM #9
Professional Member*
- Join Date
- Mar 2011
- Location
- Galveston Texas
- Posts
- 530
http://hvac-talk.com/vbb/showthread.php?t=186644
And i agree with moparmyway.
-
06-02-2011, 10:45 PM #10
I'm guessing earwigs in the contactor.
-
06-02-2011, 10:47 PM #11
Regular Guest
- Join Date
- Mar 2011
- Posts
- 18
Ok. Both condensing units have 120 volts coming in on both legs. When the relay closes, whether from the tstat signaling to send voltage or if I push the plunger I get 120 volts sent to the compressor, cap and fan as appropriate. My concern has been why do both these units do the exact same thing and they are so similiar in make and model. There's no reset that I know of and they are both simple units. I was hoping somebody who works on carriers could give me some advise and i guess I'm thinking too much...
-
06-02-2011, 10:49 PM #12
-
06-02-2011, 10:51 PM #13
Professional Member*
- Join Date
- Mar 2011
- Location
- Galveston Texas
- Posts
- 530
They may have 120v on both legs, but that dosen't mean they are getting full power.