    Quote Originally Posted by marter View Post
    110*/270psi
    You have to remember though with a warm box and high suction pressure you're going to be running higher than normal head and your condenser may not be in the perfect shape as it was new.


    How old is this equipment?

  2. #15
    Join Date
    Mar 2006
    Posts
    1,032
    Quote Originally Posted by dangpgt97 View Post
    You have to remember though with a warm box and high suction pressure you're going to be running higher than normal head and your condenser may not be in the perfect shape as it was new.


    How old is this equipment?
    fairly new, id say no more then 5years.. make by RDI

  3. #16
    Join Date
    Sep 2006
    Location
    Chicago
    Posts
    474
    It this the first really hot day over there?

  4. #17
    Join Date
    Dec 2009
    Location
    northeast pa
    Posts
    118
    Sounds like u are getting alot of humidity in the box.300 psi is nothing on a that hot of a day.

  5. #18
    Join Date
    Mar 2006
    Posts
    1,032
    not the first hot day, been in the mid 90 for a week or two

  6. #19
    Join Date
    Jan 2010
    Posts
    6,313
    Quote Originally Posted by marter View Post
    fairly new, id say no more then 5years.. make by RDI
    Is that low end Carrier equipment ? Probably has no head pressure control for low ambient conditions. Just fan cycling.

  7. #20
    Join Date
    Mar 2006
    Posts
    1,032
    Quote Originally Posted by VTP99 View Post
    Is that low end Carrier equipment ? Probably has no head pressure control for low ambient conditions. Just fan cycling.
    "a manitowic company" sticker was on it.
    no high pressure controls

  8. #21
    Join Date
    Dec 2009
    Location
    northeast pa
    Posts
    118
    Quote Originally Posted by marter View Post
    not the first hot day, been in the mid 90 for a week or two
    Were they stocking the freezer.Are the evap fans running the way.

  9. #22
    Join Date
    Jan 2010
    Posts
    6,313
    Quote Originally Posted by marter View Post
    "a manitowic company" sticker was on it.
    no high pressure controls
    So what happens in the winter ? Is it mild there then ?

  10. #23
    Join Date
    Mar 2005
    Location
    Pearland Texas
    Posts
    99
    In my opinion the suction pressure is too high. I work in the Houston area. I have seen freezers that would not pull down on a hot day when the condensers were on the roof. Even though the suction pressure would be close to normal the freezer wouldn't pull down. I think the condensers were minimal capacity and couldn't reject enough heat when they were on the roof.

  11. #24
    Join Date
    Mar 2006
    Posts
    1,032
    Quote Originally Posted by VTP99 View Post
    So what happens in the winter ? Is it mild there then ?
    sometimes can be mild. i dont know how this unit will cope when its cold, but for now im not concerned with that.

  12. #25
    Join Date
    Jan 2010
    Posts
    6,313
    Quote Originally Posted by marter View Post
    sometimes can be mild. i dont know how this unit will cope when its cold, but for now im not concerned with that.
    What model number do you have ? RDI does make a 120 series for high ambient conditions. They come with a larger condenser.

  13. #26
    Join Date
    Dec 2009
    Location
    northeast pa
    Posts
    118
    suction pressure is to high to be a txv.suction pressure would have to be below 10psi to feed enough liquid to raise discharge pressure.

Page 2 of 5 FirstFirst 12345 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event