Walk in freezer 404a problem
New Job. Its on of the stores ill be responsible for, anyway call came in walk in freezer at 20 degs, been at that temp all day, say it was fine before today
So I get there, verify its running, has a full sight glass, hook up gauges, 50/300, head pressure high, so i clean the coil, no change. Recover some gas (2 pounds) till i started to get bubbles in glass. head pressure still around 300.
its about 98deg ambient outside. 10deg. subcooling, let unit run for 30mins no change in box temp. Run water over condenser to get the head pressure down.
Pressure start looking better, 30/225 box cools down to 0deg, before i left.
Its got a alco style txv, this is what the other tech and I came up with a likely problem, the txv isn't feeding the coil right, and getting alot of liquid coming back up. Or there is a chance it could have some moisture in the system.
im not a full time refer guy
-
06-02-2011, 09:33 PM #2
Low side seems kind of high at 50 for a bad valve. Did you take the bulb off and warm it in hand and watch pressure?
What was the SH at the evap. SH is more importand than SC in refrigeration.If you really know how it works, you have an execellent chance of fixin' er up!
Tomorrow is promised to no one...
-
06-02-2011, 09:36 PM #3
Couple things I see... The 300psi head looks about normal for a 98* day. The suction pressure is high for a 20* box. It's hard to say what exactly is going on there. If the txv wasn't feeding or the screen was plugged you would have low suction pressure and lower than normal head pressure. This all doesn't make a lot of sense to me.
Is this a new store? Is this the first time it's ran in this hot of weather?
-
06-02-2011, 09:54 PM #4
Professional Member
- Join Date
- Mar 2006
- Posts
- 950
-
06-02-2011, 09:57 PM #5
-
06-02-2011, 10:03 PM #6
Professional Member
- Join Date
- Mar 2006
- Posts
- 950
-
06-02-2011, 10:17 PM #7
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
The recever has a dip tube that goes to the bottom to pick up liquid only. By torching the recever you will see how much liquid is in there. Should be no more then 80% when it's pumped down.
-
06-02-2011, 10:27 PM #8
Professional Member
- Join Date
- Mar 2006
- Posts
- 950
-
06-02-2011, 10:31 PM #9
I don't understand why torch the reciever? With a 98* ambient 300psi would give you a condensing temp of about 118* with 404a. He said he had a full sight glass.
-
06-02-2011, 10:35 PM #10
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
-
06-02-2011, 10:39 PM #11
Professional Member
- Join Date
- Mar 2006
- Posts
- 950
-
06-02-2011, 10:45 PM #12
-
06-02-2011, 10:49 PM #13
Professional Member
- Join Date
- Mar 2006
- Posts
- 950


Reply With Quote