    Trane wsc060 not running unless...

    you bump in the contactor.....kind of like the carriers with the clo. This unit has .6 vdc from j6 6 to 8. Is that enough for cool call? If u bump in the contactor a fewmoments later the unit starts. According to the previous tech and the maint man. I cant duplicate that but they swear to it. Runs fine in test mode

  2. #2
    Join Date
    May 2009
    Location
    Bardstown, KY
    Posts
    94
    sounds like it doesn't have enough voltage to pull in but has enough to stay in. Is it using a conventional stat? If so, how long a wire run and what gauge t-stat wire.

  3. #3
    Join Date
    Feb 2008
    Location
    Milton Florida
    Posts
    33
    Yeah wiring is fine. 26v at the coil and I havent been able to duplicate problem so for now shrugging that one off. Replaced the tstay and now have 32v dc on 6 and 8 on j6 plug...ac running fine. I may have jumped the gun on posting....thanks for reply