Thread: Mixing R22 and R410a

  1. #1
    Join Date
    May 2011
    Posts
    1
    Post Likes

    Mixing R22 and R410a

    I had a tech come and service my AC the other day and he put R410 refrigerant in in my R22 system. He said you can mix up to 20% as long as you keep the pressures in line. Is this true ? He said the real problem is the oils and when you add refrigerant you are not adding oil. Is that right ? Sounds fishy to me. Thanks in advance for your thoughts.

  2. #2
    Join Date
    Mar 2011
    Location
    Edna Bay, Alaska Highest concentration of black bears in the US
    Posts
    623
    Post Likes
    He needs to recover that charge. Then evac and recharge the unit properly. Don't run the system until it's repaired. That company will have to pay to have that refrigerant destroyed.

  3. Likes kdean1 liked this post.
  4. #3
    Join Date
    Apr 2005
    Location
    where the beer flows like wine
    Posts
    2,869
    Post Likes
    Call your tech back and ask him to put 3LB of 134a and 15.5oz of 404a and your unit will work better than ever before make sure he changes the oild to mobil 5w30

  5. Likes ksefan, hvacker liked this post.
  6. #4
    Join Date
    Jun 2004
    Location
    Location:Raleigh NC
    Posts
    10,011
    Post Likes
    NO EPA say NO

    Anyone who Know anthing about HVAC knows thats WRONG.

    A Tech like that should not be allowed to work in HVAC
    If you help others then you are a Success

  7. #5
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by hvacpope View Post
    Call your tech back and ask him to put 3LB of 134a and 15.5oz of 404a and your unit will work better than ever before make sure he changes the oild to mobil 5w30



  8. #6
    Join Date
    Jul 2007
    Location
    Mount Airy, MD
    Posts
    7,302
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    Shouldn't you be out celebrating your birthday???

    BTW, Happy Birthday !!!!

  9. #7
    Join Date
    Aug 2010
    Location
    Memphis
    Posts
    343
    Post Likes
    Dude was a dumbass.

  10. #8
    Join Date
    Jul 2008
    Location
    Denver, CO
    Posts
    4,379
    Post Likes
    It's sad companies send guys like that out to run service.

  11. #9
    Join Date
    Aug 2006
    Posts
    3,385
    Post Likes
    With those two common gases, he would be in the wrong.

    But EPA does allow you to mix,if and only if you can't get your hands on the original refrigerant.
    FEN

  12. #10
    Join Date
    Mar 2001
    Location
    Ilwaco, Washington
    Posts
    1,638
    Post Likes
    You gotta be kidding!!!!!!!!!!
    One way to outthink people is to make them think you think. They'll think you're not really thinking what you're trying to get them to think you think...........

  13. #11
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,381
    Post Likes
    that guy deserves a punch in the throat ...

  14. #12
    Join Date
    Jan 2009
    Location
    Hobart, In.
    Posts
    324
    Post Likes

    Angry You gotta be friggin kidding!







    So what if the epa allows you to mix? Are you serious? The 2 ref. couldn't be much more different. 2000 Posts and you never looked at a flash or saturation temp
    Twilly is my hero!

  15. #13
    Join Date
    Feb 2011
    Location
    Atlantic City, New Jersey
    Posts
    55
    Post Likes
    Is this guy crazy!!!!!!!!!!!

    The oils are different, the pressures are different, and the copper used to make the coils is different. Never let this close to anyone you care about ever again.

    We cannot even use the same gauges with these two refrigerants because of the differences. This is so crazy it is almost absurd!!

  16. #14
    Join Date
    May 2011
    Location
    NYC
    Posts
    23
    Post Likes
    lmao this made my day

  17. Likes ksefan liked this post.
  18. #15
    Join Date
    Jun 2006
    Location
    SW MO.
    Posts
    5,610
    Post Likes
    Quote Originally Posted by whoward View Post
    Is this guy crazy!!!!!!!!!!!

    The oils are different, the pressures are different, and the copper used to make the coils is different. Never let this close to anyone you care about ever again.

    We cannot even use the same gauges with these two refrigerants because of the differences. This is so crazy it is almost absurd!!
    Some mfr's haven't changed the copper.
    We are having problems with R410a systems leaking. They include Lennox, Amana and ADP.
    We're awl pawthetic and kweepy and can't get giwrls. That's why we fight wobots.

  19. #16
    Join Date
    Jun 2004
    Location
    Location:Raleigh NC
    Posts
    10,011
    Post Likes
    Quote Originally Posted by the mojo View Post
    With those two common gases, he would be in the wrong.

    But EPA does allow you to mix,if and only if you can't get your hands on the original refrigerant.
    NEVER heard that ?? could you please post that EPA Reg.

    Not being a $mart a$$ just NEVER heard EPA state anything like that and would like to see that reg form EPA

    THanks
    If you help others then you are a Success

  20. #17
    Join Date
    Aug 2006
    Posts
    3,385
    Post Likes
    Quote Originally Posted by fcs View Post
    NEVER heard that ?? could you please post that EPA Reg.

    Not being a $mart a$$ just NEVER heard EPA state anything like that and would like to see that reg form EPA

    THanks
    http://www.epa.gov/ozone/snap/refrig.../reftrans.html

    75% R-134a
    25% R-32 & R-125 = R-410 =R-407D
    FEN

  21. #18
    Join Date
    Jun 2004
    Location
    Location:Raleigh NC
    Posts
    10,011
    Post Likes
    Quote Originally Posted by the mojo View Post
    http://www.epa.gov/ozone/snap/refrig.../reftrans.html

    75% R-134a
    25% R-32 & R-125 = R-410 =R-407D
    OK I now understand what you thinking, however I don't believe in fact I thought EPA forbid what I call field mixing.

    Are you say EPA allows this??? is so could you show that reg.

    I would like to see reg and be able to show quote it to an EPA Rep for clarification. This would be be nice Infor to have on hand.

    Thanks
    If you help others then you are a Success

  22. #19
    Join Date
    Apr 2005
    Location
    where the beer flows like wine
    Posts
    2,869
    Post Likes
    I thought ASHRAE was the entity in charge of approving refrigerants blends. as far as I know EPA is more or less another layer of government bureaucrats gathered under the pretenses of protecting the environment.

  23. #20
    Join Date
    Jun 2004
    Location
    Location:Raleigh NC
    Posts
    10,011
    Post Likes
    Quote Originally Posted by hvacpope View Post
    I thought ASHRAE was the entity in charge of approving refrigerants blends. as far as I know EPA is more or less another layer of government bureaucrats gathered under the pretenses of protecting the environment.
    ASHRAE is a professional Society it has No legal or Regulatory authority.

    EPA,or other Federal, State, or local agencies/authorities my choice to Use/adopted ASHRAE reg it a law or code.
    If you help others then you are a Success

+ Reply to Thread
Page 1 of 4 1234 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •