  1. #1

    Mixing R22 and R410a

    I had a tech come and service my AC the other day and he put R410 refrigerant in in my R22 system. He said you can mix up to 20% as long as you keep the pressures in line. Is this true ? He said the real problem is the oils and when you add refrigerant you are not adding oil. Is that right ? Sounds fishy to me. Thanks in advance for your thoughts.

  2. #2
    Join Date
    Mar 2011
    Location
    Edna Bay, Alaska Highest concentration of black bears in the US
    Posts
    623
    He needs to recover that charge. Then evac and recharge the unit properly. Don't run the system until it's repaired. That company will have to pay to have that refrigerant destroyed.

  3. #3
    Join Date
    Apr 2005
    Location
    where the beer flows like wine
    Posts
    2,871
    Call your tech back and ask him to put 3LB of 134a and 15.5oz of 404a and your unit will work better than ever before make sure he changes the oild to mobil 5w30

  4. #4
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,930
    Quote Originally Posted by hvacpope View Post
    Call your tech back and ask him to put 3LB of 134a and 15.5oz of 404a and your unit will work better than ever before make sure he changes the oild to mobil 5w30

  5. #5
    Join Date
    Jul 2007
    Location
    Mount Airy, MD
    Posts
    7,281
    Quote Originally Posted by jpsmith1cm View Post
    Shouldn't you be out celebrating your birthday???

    BTW, Happy Birthday !!!!

  6. #6
    Join Date
    Jun 2004
    Location
    Location:Raleigh NC
    Posts
    9,667
    NO EPA say NO

    Anyone who Know anthing about HVAC knows thats WRONG.

    A Tech like that should not be allowed to work in HVAC
    If you help others then you are a Success

  7. #7
    Join Date
    Aug 2010
    Location
    Memphis
    Posts
    343
    Dude was a dumbass.

  8. #8
    With those two common gases, he would be in the wrong.

    But EPA does allow you to mix,if and only if you can't get your hands on the original refrigerant.
    FEN

  9. #9
    Join Date
    Mar 2001
    Posts
    1,529
    You gotta be kidding!!!!!!!!!!
    One way to outthink people is to make them think you think. They'll think you're not really thinking what you're trying to get them to think you think...........

  10. #10
    Join Date
    Jun 2004
    Location
    Location:Raleigh NC
    Posts
    9,667
    Quote Originally Posted by the mojo View Post
    With those two common gases, he would be in the wrong.

    But EPA does allow you to mix,if and only if you can't get your hands on the original refrigerant.
    NEVER heard that ?? could you please post that EPA Reg.

    Not being a $mart a$$ just NEVER heard EPA state anything like that and would like to see that reg form EPA

    THanks
    If you help others then you are a Success

  11. #11
    Quote Originally Posted by fcs View Post
    NEVER heard that ?? could you please post that EPA Reg.

    Not being a $mart a$$ just NEVER heard EPA state anything like that and would like to see that reg form EPA

    THanks
    http://www.epa.gov/ozone/snap/refrig.../reftrans.html

    75% R-134a
    25% R-32 & R-125 = R-410 =R-407D
    FEN

  12. #12
    Join Date
    Jun 2004
    Location
    Location:Raleigh NC
    Posts
    9,667
    Quote Originally Posted by the mojo View Post
    http://www.epa.gov/ozone/snap/refrig.../reftrans.html

    75% R-134a
    25% R-32 & R-125 = R-410 =R-407D
    OK I now understand what you thinking, however I don't believe in fact I thought EPA forbid what I call field mixing.

    Are you say EPA allows this??? is so could you show that reg.

    I would like to see reg and be able to show quote it to an EPA Rep for clarification. This would be be nice Infor to have on hand.

    Thanks
    If you help others then you are a Success

  13. #13
    Join Date
    Apr 2005
    Location
    where the beer flows like wine
    Posts
    2,871
    I thought ASHRAE was the entity in charge of approving refrigerants blends. as far as I know EPA is more or less another layer of government bureaucrats gathered under the pretenses of protecting the environment.

Page 1 of 4 1234 LastLast

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event