Page 2 of 2 FirstFirst 12
Results 14 to 16 of 16
  1. #14
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    1,498
    Quote Originally Posted by joey94 View Post
    we run our plant at 20% glycol and sometimes pull our chilled water down to 37 degrees, i was wondering if that could ever be an issue with us.
    Ok think about what you just said ......... 20% glycol and 37 degree water ......water freezes at 32degrees so why would water with 20% glycol turn to jello ?????
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    Whooo Hooo spring at last , time to get the toys out ........vrrrroooooom !!!!

  2. #15
    Join Date
    Jul 2010
    Posts
    56
    I kind of remember a 20% mixture freezing at 16 degrees.. you sounded smart and i thought you were going to come up with some scientific equation about how the glycol breaks down and at what flow and temperature.

  3. #16
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    3,384
    20% DowFrost (PG) freezes at 19.2F.
    20% DowTherm (EG) freezes at 17.9F

    if you slow your glycol flow down below the recommended minimum flow rate, the glycol next to the tubes can freeze and the glycol in the middle of the tube will not freeze. so then your chiller tries harder and gets less cooling out of it.

    i don't know about glycol breaking down, but pudding......
    The weak aren't destroyed by the strong.
    The weak are destroyed by the under-estimated.

    I know a famous song that ends in 'my nose'. The artist is dead. Know who?