    started new unit today had it running about 1 hour turnd set point up to cycle unit off went outside checked cond. went back in found indoor unit leaking thur ceiling dont know why

  2. #2
    Join Date
    Jun 2003
    Location
    Florida
    Posts
    9,546
    Post Likes
    Only one thing causes an indoor unit to leak.....water not taking the correct path out of the building.
    If everything was always done "by the book"....the book would never change.

  3. #3
    Join Date
    Sep 2005
    Posts
    4
    Post Likes
    Thread Starter

    leaking unit

    when i opened unit very little water in cond pan it also has a cond pump witch had pumped outside saw the ground was wet when i check cond shut down

  4. #4
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    Post Likes
    Model numbers,type equipment,horiz. or vrtiacal,would help.

  5. #5
    Join Date
    Mar 2005
    Posts
    997
    Post Likes
    over flow drain pan should have caught the water

  6. #6
    Join Date
    Sep 2005
    Posts
    4
    Post Likes
    Thread Starter
    unit is a 38tkb60 carrier horizotal left no over flow pan brand new unit just started checking press. temp and charge check for level chscked pump has power and worked trap installed by manufact.specs pitched toocond. pump ran unit for one hour with no water leak not to shut down

  7. #7
    Join Date
    Jun 2003
    Location
    Florida
    Posts
    9,546
    Post Likes
    O.K. if water is flowing outside, that means the drainpan plug was removed. I've seen this on horizontal units we had.....check your static pressures/ airflow, as water will blow off the coil into the evap unit and then leak out.
    If everything was always done "by the book"....the book would never change.

  8. #8
    Join Date
    Sep 2005
    Posts
    4
    Post Likes
    Thread Starter

    unit leaking

    just wanted to say thanks i will do some air balancein tomorrow