Mitsubishi CityMULTI
Results 1 to 8 of 8
  1. #1
    Join Date
    May 2011
    Location
    Amarillo Texas
    Posts
    11

    Mitsubishi CityMULTI

    Last week I installed my first CityMULTI system in this small church. Its purring like a kitten now but I had major problems with the BC control box. Well I should say the port/isolation valves pos that were supplied in the kit. Has anyone ran into this

  2. #2
    NOT SURE WHAT YOU ARE ASKING ARE YOU ASKING ABOUT THE BALL VALVE THAT SHOULD BE INSTALLED AT EACH PORT OR THE SOLENOID VAVES IN THE BC ITSELF .

  3. #3
    Join Date
    May 2011
    Location
    Amarillo Texas
    Posts
    11

    Confused

    Quote Originally Posted by Jersey Boy View Post
    NOT SURE WHAT YOU ARE ASKING ARE YOU ASKING ABOUT THE BALL VALVE THAT SHOULD BE INSTALLED AT EACH PORT OR THE SOLENOID VAVES IN THE BC ITSELF .
    My bad its the ball valve......I think they all leak. I tested from all of eight indoor units: unit/line set/ ball valve @ BC controller with the 300 psi (N) and no one lineset held over 14 hours. Ok, I went ahead and and plumbed the BC (1"5/8) to the out door and made my second overnight test. From BC ball valve I agian hit the lineset with 300 psi (N). The valves leaked and all eight linesets to BC dropped to 150 <> psi...... however from BC to Outdoor had raised to cominsate (they equilized). My new ?'s: have you ever ran into this? Am I in the wrong field?

  4. #4
    FIRST OFF 300 # NITROGEN IS NOT ENOUGH MANUF. WANTS 600# FOR 24 HRS . YOU WILL NEED TO PURCHASE BALL VALVES RATED AT SOME ARE 700 BUT LOOK FOR 800 PSI . AND YES HAVE RAN INTO THIS BEFORE WITH BALL VALVES AND ALSO DO YOURSELF A FAVOR AND REPLACE ALL SCHRADER CORES WHILE YOU ARE AT IT AS THEY SEEM TO LEAK AFTER THE 600 PSI GET TO THEM . READ THE INSTRUCTIONS AND FOLLOW TO THE T" AND YOU WILL NOT HAVE AN ISSUE . IT IS IMPORTANT TO BE CLEAN , DRY AND TIGHT ON THESE SYSTEM WITHOUT EXCEPTION . IF YOU DO NOT BELIEVE IT AFTER YOUR FIRST FILTER RESTRICTION CHANGEOUT DUE TO TRASH YOU WILL BE A BELEIVER .

  5. #5
    Join Date
    Apr 2007
    Location
    Pa
    Posts
    758
    what is the location of the leak?? at the packing?? or is it pitted? call the rep if it is pitted and raise hell and make his rear pay for it and the labor to repair!

  6. #6
    Join Date
    Jul 2006
    Posts
    14
    Did several and never had issues with the ball valves leaking. The over abundance of flair joints was another issue. Wish mits left more room to sweat ball valves on. They want 500# or more for over 24hrs or they may not warranty the unit.

  7. #7
    Join Date
    Jun 2004
    Posts
    246
    I know they want 600psi but I think that's too much. I have ran into schraders leaking. Just replaced six yesterday. They were all leaking bad. I agree I would love to cut all flares off and braze everything in.

  8. #8
    Join Date
    Aug 2011
    Location
    Ohio
    Posts
    10
    Quote Originally Posted by nun View Post
    I know they want 600psi but I think that's too much. I have ran into schraders leaking. Just replaced six yesterday. They were all leaking bad. I agree I would love to cut all flares off and braze everything in.
    Diakin uses wrenches specified for the correct torque for each flare connection. I've used them for mitsubishi installs and never had leaks on the flares. Just a suggestion.