best way to repair 1/8 cap tube?
i have got a leak coming from a cap tube, should i just replace the whole section or repair it? never had to do one before, thanks for any help!!
-
05-27-2011, 10:29 PM #2
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
-
05-27-2011, 10:30 PM #3
I think I would try Stay Brite on it. What do you have to loose. If it does not work, you get to find out how to change a cap tube.
-
05-27-2011, 10:35 PM #4
Professional Member
- Join Date
- Apr 2011
- Posts
- 53
-
05-27-2011, 10:42 PM #5
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
-
05-27-2011, 10:46 PM #6
If it is actually a cap tube, as in part of a metering device, replace the entire assembly.
If it is a distribution tube, do not try to fill in the hole, you will just block it up.
If it is not already broken apart, gently bend it back and forth to break it apart. Then slide about a 3" piece of 1/4" tubing over the two ends evenly, crimp down on the ends of the 1/4" tubing without crushing the distribution tube and braze.Government is a disease......masquerading as its own cureEcclesiastes 10:2 NIV
-
05-28-2011, 11:31 PM #7
Professional Member
- Join Date
- Jun 2006
- Posts
- 173
iv'e done the same as roboteq,and as vtp99 said "you will not need much heat". i'll use my map gas torch but with silfoss.
-
05-29-2011, 01:50 AM #8
Yup the 1/4 inch thing works. I have done it on a cap tube metering device as well with success - you aren't reducing the length of the tube so you still get the required pressure drop across it - even with the "gap" you just installed. Just make sure you get a good clean cut on the cap tube and don't pinch the ends shut.
-
05-29-2011, 02:02 AM #9
-
05-29-2011, 03:58 AM #10
-
05-29-2011, 07:37 AM #11
-
05-29-2011, 01:47 PM #12
-
05-30-2011, 11:43 PM #13
Yea, I've done that too. But sometimes it screws up the system pressures. If you do this type of repair make sure its outside the box, if its inside it messes with the restriction because of that "pocket" of low pressure. JMO. Either that or it collects oil? I just know it works better outside the box. Whenever possible I just change the cap tube. Less call back potential...
I r the king of the world!...or at least I get to stand on the roof and look down on the rest of yall


Reply With Quote
u must deal with this all the time eh? thanks guys