    Copeland Digital Scroll Failures
    Seems all of a sudden (in the past month) we are seeing multiple compressor failures on digital scrolls on different jobs, all Aaon equipment. Anyone else experiencing this ?
    J
    Nov 2007
    Central Alabama
    We had 6 Aaon heat pumps installed last summer with digital scrolls. Four out of the six compressors failed within a week of startup. According to the factory rep the accumulators were piped backwards, and the failure was due to no oil returning to the compressors. Aaon sent two guys down who repiped the accumlators and replaced the compressors. No problems since.
    Mar 2011
    Louisiana
    Were these split system heat pumps or packaged units?
    J
    Nov 2007
    Central Alabama
    The ones I had were package RTU's
    Mar 2011
    Louisiana
    I am seeing both packaged units from the Aaon Tulsa factory and Chillers from their Longview factory.
    J
    We had an aaon rtu digital scroll fail as well, noisy little things to.