    Copeland Digital Scroll Failures

    Seems all of a sudden (in the past month) we are seeing multiple compressor failures on digital scrolls on different jobs, all Aaon equipment. Anyone else experiencing this ?

    J
    Last edited by Jarreau; 05-26-2011 at 04:34 PM. Reason: typo

  2. #2
    Join Date
    Nov 2007
    Location
    Central Alabama
    Posts
    42
    We had 6 Aaon heat pumps installed last summer with digital scrolls. Four out of the six compressors failed within a week of startup. According to the factory rep the accumulators were piped backwards, and the failure was due to no oil returning to the compressors. Aaon sent two guys down who repiped the accumlators and replaced the compressors. No problems since.

  3. #3
    Join Date
    Mar 2011
    Location
    Louisiana
    Posts
    120
    Were these split system heat pumps or packaged units?

    J

  4. #4
    Join Date
    Nov 2007
    Location
    Central Alabama
    Posts
    42
    The ones I had were package RTU's

  5. #5
    Join Date
    Mar 2011
    Location
    Louisiana
    Posts
    120
    I am seeing both packaged units from the Aaon Tulsa factory and Chillers from their Longview factory.

    J

  6. #6
    Join Date
    Jul 2006
    Posts
    14
    We had an aaon rtu digital scroll fail as well, noisy little things to.