    why do bubbles in the sight mean low on refrigerant charge I don't understand how that works. I was also told that on start up you'll get bubbles in the sight glass why is that.
    Indiana
    Quote Originally Posted by bojolad77 View Post
    why do bubbles in the sight mean low on refrigerant charge .
    another rule of thumb that is not necessarily true
    Dec 2008
    "Bay Area", Cali
    its basicly acting like a "metering device"
    refer is flashing off into the sight glass becuase of the increase of the space in the sight glass compared to the liquid line
    SMW 104
    In my opinion, a sight glass is useless on R-22 A/C units, unless it has a moisture indicator, they are good for that I suppose.
    Hey cockroach, don't bug me! ©
    In order to properly function, a TXV requires a solid column of liquid refrigerant entering it.
    A sight glass provides a quick glance into the system and, on some equipment, can allow a quick verification of charge.
    It shouldn't always be wholly relied on, though. There are other ways of verifying charge that are more accurate.
    South Texas
    On some systems under the right conditions the presence of bubles in the sight glass can be considered normal. Was on a job once where someone had put a sight glass on a package unit, found out they had grossly overcharged the system.
    Rochester, NY, USA
    Quote Originally Posted by Diceman View Post
    Quote Originally Posted by SouthTex View Post
    as these guys said:
    you should never put a sight glass on a residential a/c system.
    why? Glad you asked. Because many "newbies"(and even some old timers) believe if they see bubbles in a sight glass the system is under charged. If you charge a system properly, there is a good chance your going to see bubbles in the sight glass on a 72°-78° day. If you come back on a 90° day the bubbles will be gone.
    Use proper techniques for checking the charge of a system, DO NOT rely on a sight glass.
    everytime I come across a system with a sight glass, the damn thing is over charged, every single time. People get lazy and don't check using superheat and subcool, then you have problems
    Measure Twice
    CUT ONCE
    Crap, throw that away and get a beer
    South Carolina
    I put a sight glass in my system when I installed it in my home because I wanted a method of checking the condition of the refrigerant through visual inspection and to monitor for the presence of moisture.
    Bubbles don't mean a loss of charge, proper technique is the only thing that can provide that diagnosis but, sight glasses have their uses.
    “Two things are infinite: the universe and human stupidity; and I’m not sure about the universe.” —Albert Einstein
    Rochester, NY, USA
    Quote Originally Posted by william antley View Post
    only if you know what your looking at.
    Joe HomeOwner doesn't have a clue and when HE see bubbles, he's going to think the system is under charged or that something is wrong.
    For you! ya maybe a sight glass has some value, but generally speaking, in a residential system a sight glass is not a good idea