Thread: Inline fuse
    Cincinnati Ohio
    I'm working on a 2.5 ton rheem ac unit. There is a inline fuse after the transfomer and before the computer board. I have 124v on the line side and 27v @ the transformer. the unit will run for 12 hours then blow the inline fuse if it is replaced it will run for another 12 hours then blow. The transformer has been replaced and i'm still pulling 27v is the bouard bad or a'm I getting a voltage spike.
    Cribbetr
    Houston,Tx.
    Thanks Cribbetr
    I don't believe it was ever a transformer issue might start checking your low voltage wires for shorts and could also be the 24 volt coil in your contactor outside, could be the board but I doubt it.
    Florida
    Do you have the correct size fuse? Only a Short/ high amp draw will cause the fuse to blow...check wires&connections.
    Huntsville,AL
    switch to Slo-Blow type
    transformer VA rating?
    you will also protect the transformer by having fuse in 120v!
    be aware that the 0.25x1.25" fuses are rated 32V above 8 amperes! -- unless ceramic -- most electronic distributors carry them --
    or HOSFELT.com
    Feb 2005
    Dothan, Al
    My quess is the board is bad - heating up for twelve hours, causing slow incease in current draw until fuse blows - possible caused by 'tracking' across the 'lands' or just s chip overheating.
    Hope this helps,
    Richard