Results 1 to 7 of 7
    May 2011
    Vietnam
    Ventilating fan calculation
    Dear HVAC experts,
    What is the first important thing to be considered when doing calculation for ventilation fan?
    Lancaster PA
    Knowing why your ventilating.
    Is it for fresh air, or cooling. Need to know that to know how much air you need to move.
    SW FL
    TYPE - Residential, Commerical, Institutional
    # of people - House, Movie Theater, Church
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art".
    May 2011
    Vietnam
    It is for a room contained several electrical panels and it is coomercial ventilating.
    I have not yet known how much air I need to move. But what is the next step to think of? Measuring the room temperature?
    Rochester NY
    You answered type, but not why or how much. What is the problem you are solving?
    Boise, ID
    Quote Originally Posted by hien.nguyenquoc View Post
    Next thing you need to figure out is the total heat gain into the room from walls and equipment.
    After that you need to know what temperature the room needs to be. Then, know what temperature you have available, presuming you are relying on exhaust air from an adjacent space. With the above, you can do thecalculate the required CFM.
    If a nation expects to be ignorant and free, in a state of civilization, it expects what will never be. (Thomas Jefferson 1816)
    SW FL
    Question What electrical panels ? Do they produce heat?
    It is for a room contained several electrical panels and it is commercial ventilating.
    K.I.S.S.
    1
    How much heat (Q - BTU/Hr) do the panels produce?
    2
    What is the source of "cool air" that can be used?
    What is the temperature of the "cool air" (Tc) ?
    3
    What is the upper temperature limit (Th) of any components in the room that is being ventilated?
    Q = dT * CFM * constant
    Constant might be close to 1.0 or up to ~ 1.07
    CFM = Q / dT
    ___ = Q / ( Th -Tc)
    Designer Dan