  1. #27
    Join Date
    Feb 2008
    Location
    Ma.
    Posts
    269
    well go the compressor in., the system vacuumed and about 75%of factory charge in.... to find no suction pressure... looks like I have to find a restriction... had 135 high side with 0 low side with and no ccpr ajdusments help

  2. #28
    Join Date
    Jan 2010
    Posts
    5,812
    Quote Originally Posted by JF254 View Post
    well go the compressor in., the system vacuumed and about 75%of factory charge in.... to find no suction pressure... looks like I have to find a restriction... had 135 high side with 0 low side with and no ccpr ajdusments help
    If you went with MP66 (R401b) don't panic just yet. @ 1/2 psig. your temp. is -20*
    And your discharge looks good to depending on the ambient @ the condenser coil.

  3. #29
    Join Date
    Feb 2008
    Location
    Ma.
    Posts
    269
    even with a 74 degree box?

  4. #30
    Join Date
    Mar 2007
    Location
    wedged in freezer shelf
    Posts
    6,123
    Cap tube?
    What gas did you put in?
    We are not mind readers

    Still seems short on charge. could be around 25%
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  5. #31
    Join Date
    Feb 2008
    Location
    Ma.
    Posts
    269
    mp 66
    cap tube.
    new filter drier (no temp drop)
    called up traulse got the specs for the cap tube.. they want .049 all I can find is .050....

    is mp66 100% of charge on r12? I was going to start at 75 and work my way up.

  6. #32
    Join Date
    Jan 2010
    Posts
    5,812
    Quote Originally Posted by JF254 View Post
    even with a 74 degree box?
    How long did you let it pull down ? It's going to take some time with a cap tube.
    Did the fans come on ?
    What's the frost pattern on the coil ?

  7. #33
    Join Date
    Feb 2008
    Location
    Ma.
    Posts
    269
    ran it for 20 min. the fans never came on... every once in a while I would get a suction of4-5 psi and it would start getting cold and the just bottom right out to zero. ambient at the coil was 80 (off the top of my head)

  8. #34
    Join Date
    Aug 2007
    Location
    Winter Haven, FL
    Posts
    3,584
    20mins might not have been long enough.

  9. #35
    Join Date
    Feb 2008
    Location
    Ma.
    Posts
    269
    Quote Originally Posted by Joe Harper View Post
    20mins might not have been long enough.
    I was starting think that after he asked.....

  10. #36
    Join Date
    Aug 2007
    Location
    Winter Haven, FL
    Posts
    3,584
    Your fans might have come on for a very short time. You might need to pull the fan delay switch and test it.

  11. #37
    Join Date
    Aug 2006
    Location
    st.petersburg,fl
    Posts
    776

    Lightbulb

    If you took your SH & SC readings you could end the guessing game

    Hope this Helps....
    Isn't sanity just a one-trick pony anyway? I mean, all you get is that one trick, rational thinking, but when you're good and crazy, well, the sky's the limit!

  12. #38
    Join Date
    Feb 2008
    Location
    Ma.
    Posts
    269
    not guessing at all subcooling of 11 and superheat of 78

  13. #39
    Join Date
    Aug 2006
    Location
    st.petersburg,fl
    Posts
    776

    Lightbulb

    You are low on refrigerant...

    Hope this Helps...
    Isn't sanity just a one-trick pony anyway? I mean, all you get is that one trick, rational thinking, but when you're good and crazy, well, the sky's the limit!

Page 3 of 5 FirstFirst 12345 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event